Citeren Luiz Angelo Daros de Luca <[EMAIL PROTECTED]>:
> However, as the nominal battery is 240V, NUT battery graphic is not very
> useful. I uses an scale up to 240V and
> 2.27V (AC on) or 2.0xV (AC off) is not visible. If I divide the nominal
> voltage (hack) by 120, NUT avoids to generate a graphic.
> The only situation that looks better was when I multiplied 2.xx by 120. I
> also tested dividing nominal voltage by 20 and multipling battery voltage by
> 6 to get 12V but I think this is worse as it's not equal to neither values
> (and needs two modifications).
You could try running the version from the trunk. This allows setting
the (undocumented for the moment)
override.battery.voltage.nominal = 2
in ups.conf.
> Which solution is the best? Hack the graphics, the nominal voltage or the
> voltage measure? There is an LCD in front of the UPS that shows some
> information and it does the "120 times" trick with the battery voltage.
This really should be fixed in the driver.
Best regards, Arjen
--
Please keep list traffic on the list
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev