Citeren Daniel O'Connor <[email protected]>:

I have had a long standing problem with NUT talking to 110V MGE UPSs on
FreeBSD, I was recently investigating again and noticed that upsd seems
overly noisy, eg..

May  5 03:50:36 egbert upsd[96662]: UPS [ups1] data is no longer stale
May 5 03:50:36 egbert upsd[96662]: Data for UPS [ups1] is stale - check driver
May  5 03:50:36 egbert upsd[96662]: UPS [ups1] data is no longer stale
May 5 03:50:36 egbert upsd[96662]: Data for UPS [ups1] is stale - check driver
May  5 03:50:39 egbert upsd[96662]: UPS [ups1] data is no longer stale
May 5 03:50:46 egbert upsd[96662]: Data for UPS [ups1] is stale - check driver
May  5 03:50:46 egbert upsd[96662]: UPS [ups1] data is no longer stale
May 5 03:50:47 egbert upsd[96662]: Data for UPS [ups1] is stale - check driver
May  5 03:50:47 egbert upsd[96662]: UPS [ups1] data is no longer stale
May 5 03:50:47 egbert upsd[96662]: Data for UPS [ups1] is stale - check driver
May  5 03:50:47 egbert upsd[96662]: UPS [ups1] data is no longer stale
May 5 03:50:47 egbert upsd[96662]: Data for UPS [ups1] is stale - check driver
May  5 03:50:50 egbert upsd[96662]: UPS [ups1] data is no longer stale

ie 5 messages per second! MAXAGE is 15 seconds, IMO it should be at _least_
that time between complaints of staleness..

This has nothing to do with MAXAGE. This is the driver that is complaining about a lost connection to the UPS. The server can't do anything about that and only relays what it gets from the driver. As Arnaud has already mentioned, running the driver with debug level 3 or higher will tell you the reason why the server is logging these lines. In retrospect, it would have been better if it made a difference between the driver reporting this, or that the connection to the driver socket would be lost.

Am I misunderstanding what MAXAGE does?

Probably not. In the old days, the server would run into staleness problems for the driver socket if driver authors wouldn't call dstate_dataok() frequent enough for the server to be happy. Now that the server solicits a response from drivers (PING) at least twice before declaring them stale, this really doesn't happen anymore for most drivers. Some are still taking way too much time in upsdrv_updateinfo(), which might lead to similar problems.

Best regards, Arjen
--