2009/5/7 Daniel O'Connor <[email protected]>
> On Wed, 6 May 2009, Arnaud Quette wrote:
> > I think I've found something, but I would need an upsd debug output
> > (level 3) to see what going on the state socket.
>
> I've attached a log for you.
>
> > A few more questions:
> > - would you be able to test a patch?
>
> Yep.
>
attached, with explanation.
can you also test a real disconnection of the serial cable, and report back
if everything is ok?
cheers
Arnaud
--
Linux / Unix Expert R&D - Eaton - http://www.eaton.com/mgeops
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.free.fr/
--- drivers/mge-shut.c (révision 1840)
+++ drivers/mge-shut.c (copie de travail)
@@ -187,7 +187,12 @@
if (commstatus == 0) {
if (shut_ups_start () != 0) {
upsdebugx(2, "No communication with UPS, retrying");
- dstate_datastale();
+ /* don't bit the UPS to death. using that protocol,
+ * units tends to be "flooded" temporarily under some
+ * circustances (battery test, autonomy recalc., ...).
+ * we leave to upsd to declare the device staled!
+ * dstate_datastale(); */
+ sleep(2);
return;
} else {
upsdebugx(2, "Communication with UPS established");
@@ -226,10 +231,11 @@
dstate_setinfo(item->type, item->fmt, hValue);
dstate_dataok();
- } else {
+ } /* don't bit the UPS to death. see above
+ * else {
if (shut_ups_start () != 0)
dstate_datastale();
- }
+ }*/
}
}
}
_______________________________________________
Nut-upsdev mailing list
[email protected]