I'm not sure I understand your question. The UPS was running for more than 15 minutes before it went below the battery.charge.low: of 70.
Below is my /etc/nut/nut.conf. My goal is that when the UPS report a battery.charge.low of < 70 (or, if possible has been running for 5 minutes) it starts the shutdown process. The shutdown process should take 15 minutes so that proxmox can shutdown guests and then safely shut down itself.. Thanks root@proxmox-01:~# cat /etc/nut/nut.conf # Network UPS Tools: example nut.conf # ############################################################################## # General section ############################################################################## # The MODE determines which part of the NUT is to be started, and which # configuration files must be modified. # # This file try to standardize the various files being found in the field, like # /etc/default/nut on Debian based systems, /etc/sysconfig/ups on RedHat based # systems, ... Distribution's init script should source this file to see which # component(s) has to be started. # # The values of MODE can be: # - none: NUT is not configured, or use the Integrated Power Management, or use # some external system to startup NUT components. So nothing is to be started. # - standalone: This mode address a local only configuration, with 1 UPS # protecting the local system. This implies to start the 3 NUT layers (driver, # upsd and upsmon) and the matching configuration files. This mode can also # address UPS redundancy. # - netserver: same as for the standalone configuration, but also need # some more network access controls (firewall, tcp-wrappers) and possibly a # specific LISTEN directive in upsd.conf. # Since this MODE is opened to the network, a special care should be applied # to security concerns. # - netclient: this mode only requires upsmon. # # IMPORTANT NOTE: # This file is intended to be sourced by standard POSIX shell scripts (so # there is no guaranteed `export VAR=VAL` syntax) and by systemd on Linux. # You MUST NOT use spaces around the equal sign! MODE=netserver # Uncomment this to allow starting the service even if ups.conf has no device # sections at the moment. This environment variable overrides the built-in # "false" and an optional same-named default flag that can be set in upsd.conf: #ALLOW_NO_DEVICE=true #export ALLOW_NO_DEVICE root@proxmox-01:~# cat nano /etc/nut/ups.conf cat: nano: No such file or directory # Network UPS Tools: example ups.conf # # --- SECURITY NOTE --- # # If you use snmp-ups and set a community string in here, you # will have to secure this file to keep other users from obtaining # that string. It needs to be readable by upsdrvctl and any drivers, # and by upsd. # # --- # # This is where you configure all the UPSes that this system will be # monitoring directly. These are usually attached to serial ports, but # USB devices and SNMP devices are also supported. # # This file is used by upsdrvctl to start and stop your driver(s), and # is also used by upsd to determine which drivers to monitor. The # drivers themselves also read this file for configuration directives. # # The general form is: # # [upsname] # driver = <drivername> # port = <portname> # < any other directives here > # # The section header ([upsname]) can be just about anything as long as # it is a single word inside brackets. upsd uses this to uniquely # identify a UPS on this system. # # If you have a UPS called snoopy, your section header would be "[snoopy]". # On a system called "doghouse", the line in your upsmon.conf to monitor # and manage it would look something like this: # # MONITOR snoopy@doghouse 1 upsmonuser mypassword primary # # It might look like this if monitoring in "secondary" mode (without any # ability to directly manage the UPS) from a different system: # # MONITOR snoopy@doghouse 1 upsmonuser mypassword secondary # # Configuration directives # ------------------------ # # These directives are used by upsdrvctl only and should be specified outside # of a driver definition: # # maxretry: OPTIONAL. Specify the number of attempts to start the driver(s), # in case of failure, before giving up. A delay of 'retrydelay' is # inserted between each attempt. Caution should be taken when using # this option, since it can impact the time taken by your system to # start. # # The built-in default is 1 attempt. # # retrydelay: OPTIONAL. Specify the delay between each restart attempt of the # driver(s), as specified by 'maxretry'. Caution should be taken # when using this option, since it can impact the time taken by your # system to start. # # The default is 5 seconds. # # chroot: OPTIONAL. Used for securing. See man page for details. # # driverpath: OPTIONAL. Used for custom setups. See man page for details. # # nowait: OPTIONAL. Tell upsdrvctl to not wait at all for the driver(s) # to execute the requested command. Fire and forget. # # pollinterval: OPTIONAL. The status of the UPS will be refreshed after a # maximum delay which is controlled by this setting (default # 2 seconds). This may be useful if the driver is creating too # much of a load on your system or network. # Note that some drivers also have an option called *pollfreq* # which controls how frequently some of the less critical # parameters are polled. See respective driver man pages. # # Set maxretry to 3 by default, this should mitigate race with slow devices: maxretry = 3 # These directives can be set outside and inside a driver definition, with # slightly different meanings per context: # # maxstartdelay: OPTIONAL. This can be set as a global variable # above your first UPS definition and it can also be # set in a UPS section. This value controls how long # upsdrvctl will wait for the driver to finish starting. # This keeps your system from getting stuck due to a # broken driver or UPS. # The default is 45 seconds. # # debug_min: OPTIONAL. Specify a minimum debug level for all driver daemons # (when specified at global level), or for this driver daemon # (when specified in a driver section), e.g. for troubleshooting # a deployment. This does not directly impact the foreground or # background running mode. If both the global and driver level # `debug_min` are set, the driver-level setting takes precedence. # Command-line option `-D` can only increase this verbosity level. # # user, group: OPTIONAL. Overrides the compiled-in (also global-section, # when used in driver section) default unprivileged user/group # name for NUT device driver. Impacts access rights used for # the socket file access (group) and communication ports (user). # # synchronous: OPTIONAL. The driver work by default in asynchronous # mode (like *no*) with fallback to synchronous if sending # fails (i.e *synchronous=auto*). This means that all data # are pushed by the driver on the communication socket to # upsd (Unix socket on Unix, Named pipe on Windows) without # waiting for these data to be actually consumed. With # some HW, such as ePDUs, that can produce a lot of data, # asynchronous mode may cause some congestion, resulting in # the socket to be full, and the driver to appear as not # connected. By enabling the 'synchronous' flag # (value = 'yes'), the driver will wait for data to be # consumed by upsd, prior to publishing more. This can be # enabled either globally or per driver. # # The default is 'no' (i.e. asynchronous mode) for backward # compatibility of the driver behavior. # # These directives are common to all drivers that support ups.conf: # # driver: REQUIRED. Specify the program to run to talk to this UPS. # apcsmart, bestups, and sec are some examples. # # port: REQUIRED. The serial port where your UPS is connected. # /dev/ttyS0 is usually the first port on Linux boxes, for example. # # sdorder: OPTIONAL. When you have multiple UPSes on your system, you # usually need to turn them off in a certain order. upsdrvctl # shuts down all the 0s, then the 1s, 2s, and so on. To exclude # a UPS from the shutdown sequence, set this to -1. # # The default value for this parameter is 0. # # desc: optional, to keep a note of the UPS purpose, location, etc. # # nolock: optional, and not recommended for use in this file. # # If you put nolock in here, the driver will not lock the # serial port every time it starts. This may allow other # processes to seize the port if you start more than one by # mistake. # # This is only intended to be used on systems where locking # absolutely must be disabled for the software to work. # # ignorelb: OPTIONAL. Ignore low battery condition reported by device, # and evaluate remaining battery charge or runtime instead. # See man page for details. # # usb_set_altinterface(=num): OPTIONAL. Require that NUT calls this method # to set the interface, even if 0 (default). Some devices require # the call to initialize; others however can get stuck due to it - # so it is not called by default. Yet others can be composite # devices which use a non-zero interface to represent the UPS. # # default.<variable>: OPTIONAL. Set a default value for <variable> which is # used in case the UPS doesn't provide a value, but which will be # overwritten if a value is available from the UPS, e.g.: # default.input.voltage.nominal = 230 # will report the nominal input voltage to be 230, unless the UPS # eventually tells us differently. # # override.<variable>: OPTIONAL. Set a value for <value> that overrides # (for NUT) any value that may be read from the UPS. # Used for overriding values from the UPS that are clearly wrong # (e.g. some devices report wrong values for battery voltage): # override.battery.voltage.nominal = 12 # Use with caution! This will only change the appearance of the # variable to the outside world (and NUT calculations), internally # in the UPS the original value is used. # # Anything else is passed through to the hardware-specific part of # the driver. # # Examples # -------- # # A simple example for a UPS called "powerpal" that uses the blazer_ser # driver on /dev/ttyS0 is: # # [powerpal] # driver = blazer_ser # port = /dev/ttyS0 # desc = "Web server" # # If your UPS driver requires additional settings, you can specify them # here. For example, if it supports a setting of "1234" for the # variable "cable", it would look like this: # # [myups] # driver = mydriver # port = /dev/ttyS1 # cable = 1234 # desc = "Something descriptive" # # To find out if your driver supports any extra settings, start it with # the -h option and/or read the driver's documentation. offdelay = 120 ondelay = 240 [pve1] driver = "usbhid-ups" port = "auto" vendorid = "06DA" productid = "FFFF" desc = "Phoenixtec Power Co., Ltd Innova Unity" serial = "CPANM2436540037" override.battery.charge.low = 70 override.battery.runtime.low = 2500 # wait 5 minutes for ups to power off override.ups.delay.shutdown = 300 On Sat, 1 Jun 2024 at 19:12, Jim Klimov < [email protected]> wrote: > Thinking of it, one purpose of upssched is to delay reaction to > short-lived flukes (e.g. if we go on battery for 20 seconds and set a delay > for 30, if we're back on line within that time frame, it is > *DuckDuckGo* did not detect any trackers. More > <https://duckduckgo.com/-RyFp-8wqBi4W1NR929X9eCjDvsVlT-oO6sD2QKxaajoOA3iCIwgi7RTLik0DrFon0odPjLs1MQSh6VLLY8FaxcDHKJDSdrhtEYMX8gKPR5K6mFIaXgB4iaWILfe01eO67Qc> > Report Spam > <https://duckduckgo.com/-RyFp-8wqBi4W1NR929X9eCjDvsVlT-oO6sD2QKxaajoOA3iCIwgi7RTLik0DrFon0odPjLs1MQSh6VLLY8FaxcDHKJDSdrhtEYMX8gKPR5K6mFIaXgB4iaWILfe01eO67Qc> > Thinking of it, one purpose of upssched is to delay reaction to > short-lived flukes (e.g. if we go on battery for 20 seconds and set a delay > for 30, if we're back on line within that time frame, it is ok to go on > living). > > I wonder if your UPS went under 70% and you aborted the experiment too > early (compared to the delay you had set, possibly with a margin for the > frequency of UPS polling rate and regular `upsmon` interactions with `upsd` > - typically 5 to 30 sec each)?.. > > Jim > > > On Sat, Jun 1, 2024 at 1:32 PM Alan via Nut-upsuser < > [email protected]> wrote: > >> Hi, >> >> A while back I set up a NUT server on a debian machine (Proxmox). I >> followed the guide at https://wiki.debian.org/Exim4Gmail so that I would >> receive email notifications and verified that emails work. >> >> I modified .*/etc/nut/upssched-cmd* and modified the script to send an >> email (happy to share). >> >> I then wanted to test the solution so I unplugged the UPS. >> NUT wrote a message to the console and I received an email to inform me >> that the UPS was on battery. >> >> I had configured the battery.charge.low: 70 and battery.runtime.low: >> 2500. My thought was when one of these conditions are met the server would >> bring down the guests and shut itself down. The UPS battery.charge went >> under 70 but nothing happened. Below is the output from upsc and what >> happened when I plugged the power back into the ups. >> >> upsc pve1@localhost >> Init SSL without certificate database >> battery.charge: 63 >> battery.charge.low: 70 >> battery.runtime: 3133 >> battery.runtime.low: 2500 >> battery.type: PbAc >> battery.voltage: 36.80 >> battery.voltage.nominal: 36.00 >> device.mfr: PHOENIXTEC >> device.model: Innova Unity >> device.serial: CPANM2436540037 >> device.type: ups >> driver.name: usbhid-ups >> driver.parameter.pollfreq: 30 >> driver.parameter.pollinterval: 2 >> driver.parameter.port: auto >> driver.parameter.productid: FFFF >> driver.parameter.serial: CPANM2436540037 >> driver.parameter.synchronous: auto >> driver.parameter.vendorid: 06DA >> driver.version: 2.8.0 >> driver.version.data: Phoenixtec/Liebert HID 0.41 >> driver.version.internal: 0.47 >> driver.version.usb: libusb-1.0.26 (API: 0x1000109) >> output.frequency: 50.00 >> output.voltage: 229.6 >> ups.delay.shutdown: 300 >> ups.load: 13 >> ups.mfr: PHOENIXTEC >> ups.model: Innova Unity >> ups.productid: ffff >> ups.serial: CPANM2436540037 >> ups.status: OB DISCHRG >> ups.vendorid: 06da >> >> *<< UPS plugged back in >>* >> >> Broadcast message from root@proxmox-01 (somewhere) (Sat Jun 1 12:36:17 >> 2024): >> >> >> UPS pve1@localhost on line power >> >> How can I diagnose / resolve this? >> >> Thanks >> Alan >> >> >> _______________________________________________ >> Nut-upsuser mailing list >> [email protected] >> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser >> >
_______________________________________________ Nut-upsuser mailing list [email protected] https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser