On Sat, 1 Jun 2024, Alan via Nut-upsuser wrote:

root@proxmox-01:~# cat nano /etc/nut/ups.conf

If you send us hundreds of lines of comments it makes your post difficult to understand. Could you trim out the comments with for example

 cat /etc/nut/ups.conf | grep -v "#"

which would show us the following, which is what we need to see.

maxretry = 3

offdelay = 120
ondelay = 240

[pve1]
  driver = "usbhid-ups"
  port = "auto"
  vendorid = "06DA"
  productid = "FFFF"
  desc = "Phoenixtec Power Co., Ltd Innova Unity"
  serial = "CPANM2436540037"
  override.battery.charge.low = 70
  override.battery.runtime.low = 2500
  # wait 5 minutes for ups to power off
  override.ups.delay.shutdown = 300

I don't see the line

 lowbatt = 70

which you need to make a permanent change to the value. If you use the "override", the driver will restore the default. See chapter 2.7 in https://rogerprice.org/NUT/ConfigExamples.A5.pdf

Try re-running your test with lowbatt = 70 .  Roger