On Sat, 1 Jun 2024, Alan via Nut-upsuser wrote:
root@proxmox-01:~# cat nano /etc/nut/ups.conf
If you send us hundreds of lines of comments it makes your post difficult to understand. Could you trim out the comments with for example
cat /etc/nut/ups.conf | grep -v "#" which would show us the following, which is what we need to see.
maxretry = 3 offdelay = 120 ondelay = 240 [pve1] driver = "usbhid-ups" port = "auto" vendorid = "06DA" productid = "FFFF" desc = "Phoenixtec Power Co., Ltd Innova Unity" serial = "CPANM2436540037" override.battery.charge.low = 70 override.battery.runtime.low = 2500 # wait 5 minutes for ups to power off override.ups.delay.shutdown = 300
I don't see the line lowbatt = 70which you need to make a permanent change to the value. If you use the "override", the driver will restore the default. See chapter 2.7 in https://rogerprice.org/NUT/ConfigExamples.A5.pdf
Try re-running your test with lowbatt = 70 . Roger
_______________________________________________ Nut-upsuser mailing list [email protected] https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser