Carlos Rodrigues wrote:
Measuring the voltages just means letting the UPS charge completely
(until the bundled software says 100%) and then see what value NUT
reports for "battery.voltage", and then unplugging the UPS from the
wall until it goes into low battery, and check again the voltage that
NUT is reporting.
Here are the values
- 100% battery charge, status normal: battery.voltage: 2.3
- 25% battery charge, upsilon reports "batt low", the UPS is beeping,
shutdown triggered: battery.voltage: 1.8
full data provided by upsc before shutting down follows:
[EMAIL PROTECTED] ~]# upsc [EMAIL PROTECTED]
battery.charge: 0.0
battery.voltage: 1.8
battery.voltage.nominal: 96.0
driver.name: megatec
driver.parameter.port: /dev/ttyS0
driver.version: 2.1.0
driver.version.internal: 1.4
input.frequency: 0.0
input.voltage: 0.0
input.voltage.fault: 190.0
output.voltage: 221.3
output.voltage.nominal: 220.0
ups.delay.shutdown: 2
ups.delay.start: 3
ups.load: 49.0
ups.mfr: Ablerex
ups.model: MS3000RT MS02035C
ups.serial: unknown
ups.status: OB LB
ups.temperature: 41.0
Anything else I can help with ?