Charles Lepple wrote:
> On 7/25/07, Stuart Rackham <[EMAIL PROTECTED]> wrote:
>> Hi
>>
>> I'm having a  problem with the bcmxcp_usb driver FSD command: everything
>> seems to work apart from:
>>
>>    upsmon -c fsd
>>
>> Environment: Ubuntu 7.04, nut 2.0.5-1, nut-usb 2.0.5-1, Powerware 3105
>> UPS.
>>
>> upsd appears to send the FSD command to the UPS, upsmon then runs my
>> NOTIFYCMD (which halts my PC) but the UPS just doesn't turn off.
>> Here are the /var/log/daemon.log entries:
> 
> I have seen a similar problem with usbhid-ups on an MGE Pulsar
> Evolution with Ubuntu 7.04. The machine shuts down on the LB signal,
> but the UPS stays on.
> 
> My suspicion is that there is something in the Ubuntu shutdown
> procedure that is killing the driver (or upsd) before it can send the
> shutdown command to the UPS.
> 
> I haven't had a chance to verify this, though.
> 

Thanks for the fast response Charles.

I changed the SHUTDOWNCMD to "/sbin/shutdown -H +1" which gives the
driver 1 minute to send the command but it made no difference.


Cheers, Stuart

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to