I had a similar problem with Ubuntu 6.10. There was a problem during system shutdown and the whole script was not executed. I went back to Ubuntu 6.6 and the problem went away. Check your syslog for a problem with one of the nut programs shutting down. It was happening on any shutdown not just the fsd.
Stuart Rackham wrote: > Charles Lepple wrote: > >> On 7/25/07, Stuart Rackham <[EMAIL PROTECTED]> wrote: >> >>> Hi >>> >>> I'm having a problem with the bcmxcp_usb driver FSD command: everything >>> seems to work apart from: >>> >>> upsmon -c fsd >>> >>> Environment: Ubuntu 7.04, nut 2.0.5-1, nut-usb 2.0.5-1, Powerware 3105 >>> UPS. >>> >>> upsd appears to send the FSD command to the UPS, upsmon then runs my >>> NOTIFYCMD (which halts my PC) but the UPS just doesn't turn off. >>> Here are the /var/log/daemon.log entries: >>> >> I have seen a similar problem with usbhid-ups on an MGE Pulsar >> Evolution with Ubuntu 7.04. The machine shuts down on the LB signal, >> but the UPS stays on. >> >> My suspicion is that there is something in the Ubuntu shutdown >> procedure that is killing the driver (or upsd) before it can send the >> shutdown command to the UPS. >> >> I haven't had a chance to verify this, though. >> >> > > Thanks for the fast response Charles. > > I changed the SHUTDOWNCMD to "/sbin/shutdown -H +1" which gives the > driver 1 minute to send the command but it made no difference. > > > Cheers, Stuart > > _______________________________________________ > Nut-upsuser mailing list > [email protected] > http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser > > _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser