Den Wednesday 14 January 2009 23.34.27 skrev Mathew McBride: Hi again Mathew, > On 14/1/09 9:27 AM, Arjen de Korte wrote: > > This probably needs to be multiplied by 100. Note that this value is > > reported in percentage, not a factor. Either this, or the load can't > > be right. > > It appears the UPS only provides a correct load percentage when the > inverter is on (i.e battery or switching to trim mode) > > A correct load line is: "ups.load: 17.3" > >From my PW5115. (should be the same as your T700H) # upsc pw5115 ambient.temperature: 37 battery.charge: 90 battery.runtime: 810 battery.voltage: 13.47 driver.name: bcmxcp driver.parameter.baud_rate: 9600 driver.parameter.pollinterval: 2 driver.parameter.port: /dev/ttyS0 driver.parameter.shutdown_delay: 10 driver.version: 2.3.0-1722M driver.version.internal: 0.19 input.frequency: 50.34 input.voltage: 226 output.current: 0.68 output.current.nominal: 2.27 output.frequency: 50.00 output.phases: 1 output.voltage: 226 output.voltage.nominal: 230 ups.firmware: Inve:01.04 ups.load: 39.8 ups.model: PW5115 500i 500VA ups.power: 199 ups.power.nominal: 500 ups.serial: XXXXXXXXXX ups.status: OL
Regards Kjell _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser