Den Tuesday 13 January 2009 23.27.02 skrev Arjen de Korte: Hi Arjen, > It would be nice if the driver would also report > 'battery.voltage.nominal', so that clients don't have to guess it. We > need this for instance when drawing bar graphs in the CGI programs. > That take some more time, This is in the config block. And was planned to be included when I rewrite some more.
Have to check the command list block and parse it an do something like in the upscode2 driver. The 'can_upda' and so on. So I know what the ups can respond to. But it is a binary answer and I have not find any nice way to do that. > > input.frequency: 50.34 > > input.voltage: 245 > > Same here. The input.voltage nominal is fixed. But I have to sleep. Se if I have time to enter the input/output.frequency.nominal A.S.A.P. > > This probably needs to be multiplied by 100. Note that this value is > reported in percentage, not a factor. Either this, or the load can't > be right. Now it show ups.power. But that is the output power in va. Have also input power in va and out/input.power in watt that I can read. > Although the OL status is implied when the UPS is in TRIM state, it > would be nice if the driver would report this too. Not all clients > will pick this up, if they want to know if the UPS is running on mains > or on battery (would require checking for OL|TRIM|BOOST). It helps to > be verbose here and add the OL status too. Should be fixed. I know that you have much to do, but if you have any idea about the comand- list-block, and how to parse and use it I would be glad :-) Regards Kjell _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser