Hi, 

I own one a MGE Protection Center 675. You can change the
parameter ups.delay.start into your UPS to set the "Interval to wait
before (re)starting the load (seconds)" 

use upsset to change the
value. 

Regards,
René 

Le 2013-12-06 15:14, Angel Tsankov a écrit :


> Hello.
> 
> I am faced with a configuration where the OS (Debian
6.0.8) and the PC 
> shut down before the UPS (MGE Protection Center
675). Also, the UPS 
> restores power to attached devices as soon as
main power is back but the 
> PC does not detect power restorations that
occur less than a couple of 
> seconds, say 10, after its power supply
has been cut. As a result, if 
> main power comes back within 10 seconds
after the UPS has been shut 
> down, the UPS will power up the PC but
the latter will not start.
> 
> Does anyone have an idea how I could
handle this situation?
> 
> Regards:
> Angel Tsankov
> 
>