On 12/25/2013 12:16 AM, Kris Jordan wrote:
Angel Tsankov wrote, On 12/24/2013 1:22 AM:
[...]
I can see that my UPS (MGE Protection Center 675) has a parameter
ups.timer.start (currently holding the strange value of -10). Any idea
if this could help and how this parameter can be changed?

in upsrw?

In upsc only. Here's the complete output:

battery.charge: 100
battery.charge.low: 30
battery.runtime: 2281
battery.type: PbAc
device.mfr: MGE UPS SYSTEMS
device.model: Protection Center 675
device.serial: 1HKG25025
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 30
driver.parameter.ondelay: 60
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.data: MGE HID 1.18
driver.version.internal: 0.34
input.transfer.high: 264
input.transfer.low: 184
outlet.1.desc: PowerShare Outlet 1
outlet.1.id: 2
outlet.1.status: on
outlet.1.switchable: no
outlet.desc: Main Outlet
outlet.id: 1
outlet.switchable: no
output.frequency.nominal: 50
output.voltage: 230.0
output.voltage.nominal: 230
ups.beeper.status: enabled
ups.delay.shutdown: 30
ups.delay.start: 60
ups.load: 12
ups.mfr: MGE UPS SYSTEMS
ups.model: Protection Center 675
ups.power.nominal: 670
ups.productid: ffff
ups.serial: 1HKG25025
ups.status: OL CHRG
ups.timer.shutdown: -1
ups.timer.start: -10
ups.vendorid: 0463

And here's the output from upsrw:

[battery.charge.low]
Remaining battery level when UPS switches to LB (percent)
Type: STRING
Value: 30

[input.transfer.high]
High voltage transfer point (V)
Type: STRING
Value: 264

[input.transfer.low]
Low voltage transfer point (V)
Type: STRING
Value: 184

[outlet.1.desc]
Outlet description
Type: STRING
Value: PowerShare Outlet 1

[outlet.desc]
Outlet description
Type: STRING
Value: Main Outlet

[output.voltage.nominal]
Nominal output voltage (V)
Type: ENUM
Option: "220"
Option: "230" SELECTED
Option: "240"

[ups.delay.shutdown]
Interval to wait after shutdown with delay command (seconds)
Type: STRING
Value: 30

[ups.delay.start]
Interval to wait before (re)starting the load (seconds)
Type: STRING
Value: 60

ups.timer.start --> Time before the load will be started (seconds).
Maybe it counts down after using load.on.delay?

What did you mean by "load.on.delay"?

Mine don't have the value in upsrw so it can't be set. The Eaton 5PX
(which is part MGE) I have here does have one return condition, to
return power only if the battery is charged to a certain percentage,
battery.charge.restart in upsrw.

The only UPS I've had so far that could also (always) wait a bit after
power return were APC Smart-UPS's.