Angel Tsankov wrote, On 12/6/2013 12:31 PM:
Hello, René.
You can change the parameter
ups.delay.start into your UPS to set the "Interval to wait before
(re)starting the load (seconds)"
use upsset to change the value.
So far, the ups.delay.start parameter in my MGE Protection Center 675
has always been equal to the driver.parameter.ondelay parameter (which
equals the ondelay argument in ups.conf). Furthermore, whenever I have
changed the ondelay argument in ups.conf (and restarted NUT) the above
parameters have always been set equal to ondelay. Therefore, I would
assume that ups.delay.start cannot help. Do you have any reason to
consider this assumption might be wrong?
ondelay maps to ups.delay.start, and offdelay maps to ups.delay.shutdown.
offdelay needs to be greater than ondelay. I'm using 600 & 615 on a
Win2k3 server I have connected to an Evolution 850. If the power comes
back on during the offdelay period, the ups will do a reboot cycle with
a 15s wait.
If the power is off for more than offdelay, yeah, it will turn on
instantly (*), but by then the PC has had no power for at least 15s.
The above will depend on having a good UPS.
(*) Some UPS's do provide extra options to determine when they will
restore power to load.