Hi The load issue with Diesels is most stand by diesels are started once per 
month, and run for a period of time, this is at light load.  If the Diesel is 
not worked hard the rings lose there seal ie compression falls and makes them 
hard to start.  Therefore they are load tested on various schedules for engine 
and other operating conditions,
 
Darryl  

--- On Fri, 6/18/10, Mick Abraham <[email protected]> wrote:


From: Mick Abraham <[email protected]>
Subject: Re: [RE-wrenches] Additional Battery Charger
To: "RE-wrenches" <[email protected]>
Date: Friday, June 18, 2010, 7:35 AM


I definitely like to require the generator to work hard for every hour in which 
we must listen to it, feed fuel to it, etc. (This presupposes that we have 
plenty of battery to accept genset wattage <minus altitude derations> <minus 
charger inefficiency> <minus a bit of breathing room for the engine>) 

Also: that 50 hour oil change interval...or 100 hours...or whatever...comes 
around right regular and we want to wring out lots of watt-hours between 
service dates. 

******************************

There's an old...dare I say it...wive's tale about diesel machines actually 
suffering shorter lifetimes if they are not heavily loaded. I think this belief 
goes way back to WWII days and may not be valid with current engine designs. 
It's something about the load torque requirement helping to maintain engine 
compression. Opinions from the List on this theory would be welcomed.

*******************************

Once you have plenty of charger load to throw on the generator, tweak up on the 
"AC input amps" setting in the Outback Mate or Magnum Remote while listening to 
the engine. (The battery must not be highly charged during this tweak or else 
the chargers will be in throttle back mode.) Dial up on the AC input amps 
setting while also causing major household loads (such as the water pump, 
washing machine, etc.) to kick in & out. Up, up, up until the generator engine 
can be heard to struggle beneath the load, then dial back down on the AC input 
amps until the gennie sounds happy with its work again. 

Jolliness, 

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675



On Thu, Jun 17, 2010 at 11:13 PM, benn kilburn <[email protected]> wrote:


mick, bob,


funny you should mention using a magnum as the 'additional charger', the system 
owner just happens to still have a MS4448 on the wall from his original system  
(we had upgraded his system to a FW1000 with 2 x VFX3648's back in the fall).


i hadn't even thought of using the magnum only as a charger, and the price is 
right!
thanks for the suggestion, i'll look into this as a possibility.


Any other comments on my question about generator efficiency when fully loaded 
vs say half loaded?


cheers

benn

DayStar Renewable Energy Inc. 

[email protected]
780-906-7807 
HAVE A SUNNY DAY 




From: [email protected]
To: [email protected]
Date: Thu, 17 Jun 2010 21:19:03 -0400
Subject: Re: [RE-wrenches] Additional Battery Charger






Look into the Magnum inverters as 2nd chargers, very good chargers with 
generators.
 
I have done this many times, in the case of failure of the other inverters for 
some reason, run wires and be back up and running.
I think the 4448 inverter is 60 amps @ 48 volts with an input of 16 or so amps 
AC.
 
Later,
Bob 
 


From: [email protected] 
[mailto:[email protected]] On Behalf Of benn kilburn
Sent: Thursday, June 17, 2010 7:22 PM
To: Wrenches
Subject: [RE-wrenches] Additional Battery Charger
 
G'day Wrenches,

 

 I'm looking for an additional charger(s) to increase the charging capacity 
from the back-up 12 kW Onan generator into the 1200 Ah battery.  Right now the 
generator's full potential output is limited by the charging capacity of the 
two VFX3648's which have a max charge output of 45A each.

 

The idea here is to use the generator to its full charging capacity when it is 
running, taking in to consideration that the generator will feed any AC loads 
before charging the battery. 

 

Iota and IBE chargers have been suggested.  Any comments on these or other 
makes?

 

Do all generator types (diesel, propane, LNG, gasoline) run more efficiently 
when fully loaded?  or is this only the case with diesel (so i've heard)?

 

thanks,

benn
DayStar Renewable Energy Inc. 


[email protected]

780-906-7807 

HAVE A SUNNY DAY 

 

CONFIDENTIALITY NOTICE:    This email, including any attachments, contains 
information from DayStar Renewable Energy Inc. and/or its affiliates, which may 
be confidential or privileged. The information is intended to be for the use of 
the individual or entity named above. If you are not the intended recipient, be 
aware that any disclosure, copying, distribution or use of the contents of this 
information is prohibited. If you have received this email in error, please 
notify the sender immediately by "reply to sender only" message and destroy all 
electronic and hard copies of the communication, including attachments.
 
 



Enter for a chance to get your town photo on Bing.ca! Submit a Photo Now! 





Enter for a chance to get your town photo on Bing.ca! Submit a Photo Now! 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




-----Inline Attachment Follows-----


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




      
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to