I like the fused parallel idea; could save the system, and would make battery 
troubleshooting nice.
I would suggest #6 jumpers with 50 to 60 amp breakers,  so the system could be 
operated on just a few strings if needed.

R. Walters
[email protected]
Solar Engineer




On Apr 19, 2011, at 8:29 PM, Darryl Thayer wrote:

> Batteries in parallel, How to protect from catastrophic failure.
> I just got contacted to commission a solar system off grid not of my design.  
>  Eight battery strings in parallel, AGM batteries, 24 volts @ 120 AH each 
> string (two 12 volt in series)  New system, new batteries, Silent POwer 
> Inverter.  Two kW DC array.  generator to charge through Silent power.  
> (present installer is not sure how to do final set up and testing) 
>  
> I am most concerned about 8 batteries in parallel, (especially since last 
> week a set of AGM burned up having 5 in parallel Owner had no way to break 
> the paralleling of the batteries, she could only stop the chargeing)   What I 
> am proposing for your review is requireing the installtion of  two combiner 
> boxes Midnight solar with a breaker in each battery string, using about 3' of 
> #10 to connect each battery string to the combiner box.  This way if a 
> battery failed and the paralled strings were to "dump" into the failed 
> battery it would trip the breaker.  I was thinking of using a 30 amp breaker 
> in each string. The main breaker is set at 240 amps. 
>  
> Ideas Please?  
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to