What?  No royalties?  Damn...(but thanks for the props)  Sorry I misunderstood 
what you meant.

My installs of buss bars back in the day had cable pairs of the same length but 
different pairs could be of different lengths with the consideration being bank 
construction.  I’d use slightly oversized cables to minimize resistance 
differences.  Since the cables from each string only carried current from that 
string it also made for easier installation.  In these days of grid-tie I’m 
seeing less and less discussion of batteries, good to see another one happening 
even if it was prompted by a failure, though I guess that’s how we learn.

Tom

From: R Ray Walters 
Sent: Wednesday, April 20, 2011 8:16 AM
To: RE-wrenches 
Subject: Re: [RE-wrenches] Batteries in parrallel Failure

Tom; 

That's exactly what Daryl and I were suggesting: all strings paralleled to a 
central combiner box with breakers on each series string.
The only thing I left out was that each cable set should be the same length ( 
which Daryl was already suggesting).
You need to reread what we were talking about.  We got this idea from you many 
years ago, so the record is not broken;
its been pirated, reposted for Free download on all sorts of unsavory sites, 
and you aren't getting a royalty check....
Imitation is the sincerest form of flattery, and this list listens to and 
appreciates you.

Thanks,

R. Walters
[email protected]
Solar Engineer





On Apr 19, 2011, at 10:16 PM, Tom Elliot wrote:


  The broken record will now repeat himself yet again.  Bussbars are the way to 
go, not across battery terminals but individual strings connected to a central 
positive and negative buss from which the inverter connection then runs.  This 
allows fusing of each individual connection and also allows for smaller 
positive cables and no need to have identical length parallel cables since each 
string is independently connected.  It’s what telecom installations use.  The 
Telecom guys who showed me how to do it literally laughed when told about 
paralleling across battery terminals.  They then told me they considered it 
profoundly stupid and dangerous and since I had just avoided a meltdown myself 
by catching a bad cell before complete failure I got the message pretty quick.

  Really guys, this is amazingly simple and yes, it may mean a bit more cabling 
and another component but from a safety standpoint those considerations are 
pretty minor and cheap insurance against disaster.

  Tom



  From: R Ray Walters 
  Sent: Tuesday, April 19, 2011 6:01 PM
  To: RE-wrenches 
  Subject: Re: [RE-wrenches] Batteries in parrallel Failure

  I like the fused parallel idea; could save the system, and would make battery 
troubleshooting nice. 
  I would suggest #6 jumpers with 50 to 60 amp breakers,  so the system could 
be operated on just a few strings if needed.

  R. Walters
  [email protected]
  Solar Engineer





  On Apr 19, 2011, at 8:29 PM, Darryl Thayer wrote:


    Batteries in parallel, How to protect from catastrophic failure.
    I just got contacted to commission a solar system off grid not of my 
design.   Eight battery strings in parallel, AGM batteries, 24 volts @ 120 AH 
each string (two 12 volt in series)  New system, new batteries, Silent POwer 
Inverter.  Two kW DC array.  generator to charge through Silent power.  
(present installer is not sure how to do final set up and testing) 

    I am most concerned about 8 batteries in parallel, (especially since last 
week a set of AGM burned up having 5 in parallel Owner had no way to break the 
paralleling of the batteries, she could only stop the chargeing)   What I am 
proposing for your review is requireing the installtion of  two combiner boxes 
Midnight solar with a breaker in each battery string, using about 3' of #10 to 
connect each battery string to the combiner box.  This way if a battery failed 
and the paralled strings were to "dump" into the failed battery it would trip 
the breaker.  I was thinking of using a 30 amp breaker in each string. The main 
breaker is set at 240 amps. 

    Ideas Please?  



----------------------------------------------------------------------------

    _______________________________________________
    List sponsored by Home Power magazine

    List Address: [email protected]

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm

    Check out participant bios:
    www.members.re-wrenches.org





------------------------------------------------------------------------------
  _______________________________________________
  List sponsored by Home Power magazine

  List Address: [email protected]

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org




------------------------------------------------------------------------------

  No virus found in this message.
  Checked by AVG - www.avg.com
  Version: 10.0.1321 / Virus Database: 1500/3584 - Release Date: 04/19/11

  _______________________________________________
  List sponsored by Home Power magazine

  List Address: [email protected]

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org





--------------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




--------------------------------------------------------------------------------

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1321 / Virus Database: 1500/3584 - Release Date: 04/19/11
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to