I have been using buss bars for 12 years or so and about 8 years ago started to add a class T fuse to the connection at each buss bar in most systems.
I have seen thermal runaway hit the industrial batteries I service. It would be best to avoid it in a battery box if at all possible. Do a search for buss bars or battery interconnector straps and you can locate them. I am lucky that I have a supplier that I visit and he had some lying around that he gave me. Drill them to fit the fuses and attach the cables to the fuses. If you are using a battery with a terminal you can bolt to, you can put the fuse there also. I attach the buss bars to the battery boxes with electric fence insulators as much as a standoff as anything else. I also use a board between them so there is no way to get contact between the 2 bars when working in the box. Trust me, they will spark rather well if you keep putting off wrapping the ends of the wrenches .. Also watch the ends of the cables as youre whipping them around in there too, best to wrap them with tape and pull it off when youre ready to connect them. As we all know there are lots of exposed terminals in a battery bank and only ½ of them are friendly. Using the buss bars has stopped the end cell failures that I used to see from all the batteries going to the major pos and neg terminals. I am on a useless dial up at the moment but will try a search for the buss bars when I get back to the real world. Later, Bob From: [email protected] [mailto:[email protected]] On Behalf Of Brian Teitelbaum Sent: Wednesday, April 20, 2011 2:50 PM To: RE-wrenches Subject: Re: [RE-wrenches] Batteries in parrallel Failure Does anyone know of a manufacturer or supplier of fused battery buss bars or battery string combiners (preferably using Class-T fuses) that are UL Listed for use in residential or commercial applications? Brian Teitelbaum AEE Solar From: [email protected] [mailto:[email protected]] On Behalf Of Tom Elliot Sent: Wednesday, April 20, 2011 11:36 AM To: RE-wrenches Subject: Re: [RE-wrenches] Batteries in parrallel Failure What? No royalties? Damn...(but thanks for the props) Sorry I misunderstood what you meant. My installs of buss bars back in the day had cable pairs of the same length but different pairs could be of different lengths with the consideration being bank construction. Id use slightly oversized cables to minimize resistance differences. Since the cables from each string only carried current from that string it also made for easier installation. In these days of grid-tie Im seeing less and less discussion of batteries, good to see another one happening even if it was prompted by a failure, though I guess thats how we learn. Tom From: R Ray Walters <mailto:[email protected]> Sent: Wednesday, April 20, 2011 8:16 AM To: RE-wrenches <mailto:[email protected]> Subject: Re: [RE-wrenches] Batteries in parrallel Failure Tom; That's exactly what Daryl and I were suggesting: all strings paralleled to a central combiner box with breakers on each series string. The only thing I left out was that each cable set should be the same length ( which Daryl was already suggesting). You need to reread what we were talking about. We got this idea from you many years ago, so the record is not broken; its been pirated, reposted for Free download on all sorts of unsavory sites, and you aren't getting a royalty check.... Imitation is the sincerest form of flattery, and this list listens to and appreciates you. Thanks, R. Walters [email protected] Solar Engineer On Apr 19, 2011, at 10:16 PM, Tom Elliot wrote: The broken record will now repeat himself yet again. Bussbars are the way to go, not across battery terminals but individual strings connected to a central positive and negative buss from which the inverter connection then runs. This allows fusing of each individual connection and also allows for smaller positive cables and no need to have identical length parallel cables since each string is independently connected. Its what telecom installations use. The Telecom guys who showed me how to do it literally laughed when told about paralleling across battery terminals. They then told me they considered it profoundly stupid and dangerous and since I had just avoided a meltdown myself by catching a bad cell before complete failure I got the message pretty quick. Really guys, this is amazingly simple and yes, it may mean a bit more cabling and another component but from a safety standpoint those considerations are pretty minor and cheap insurance against disaster. Tom From: R Ray Walters <mailto:[email protected]> Sent: Tuesday, April 19, 2011 6:01 PM To: RE-wrenches <mailto:[email protected]> Subject: Re: [RE-wrenches] Batteries in parrallel Failure I like the fused parallel idea; could save the system, and would make battery troubleshooting nice. I would suggest #6 jumpers with 50 to 60 amp breakers, so the system could be operated on just a few strings if needed. R. Walters [email protected] Solar Engineer On Apr 19, 2011, at 8:29 PM, Darryl Thayer wrote: Batteries in parallel, How to protect from catastrophic failure. I just got contacted to commission a solar system off grid not of my design. Eight battery strings in parallel, AGM batteries, 24 volts @ 120 AH each string (two 12 volt in series) New system, new batteries, Silent POwer Inverter. Two kW DC array. generator to charge through Silent power. (present installer is not sure how to do final set up and testing) I am most concerned about 8 batteries in parallel, (especially since last week a set of AGM burned up having 5 in parallel Owner had no way to break the paralleling of the batteries, she could only stop the chargeing) What I am proposing for your review is requireing the installtion of two combiner boxes Midnight solar with a breaker in each battery string, using about 3' of #10 to connect each battery string to the combiner box. This way if a battery failed and the paralled strings were to "dump" into the failed battery it would trip the breaker. I was thinking of using a 30 amp breaker in each string. The main breaker is set at 240 amps. Ideas Please? _____ _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org <http://www.members.re-wrenches.org/> _____ _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _____ No virus found in this message. Checked by AVG - www.avg.com <http://www.avg.com/> Version: 10.0.1321 / Virus Database: 1500/3584 - Release Date: 04/19/11 _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _____ _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _____ No virus found in this message. Checked by AVG - www.avg.com Version: 10.0.1321 / Virus Database: 1500/3584 - Release Date: 04/19/11
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org