In reference to William's comment about equalizing VRLA batteries, see page 17 of Concorde Battery's SunXtender technical manual, available online at http://www.sunxtender.com/pdfs/Sun_Xtender_Battery_Technical_Manual.pdf.
They instruct charging these AGM VRLA batteries at C/24 until 2.60 VPC is achieved, plus 4 hours, to recover from deep discharge, adding that this process can take 16 to 20 hours.
Allan

Allan Sindelar
[email protected]
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com




On 1/6/2012 11:16 AM, William Miller wrote:
Larry:

I always thought that any breach of a valve in a VRLA battery was a sign of a failure.   I recently spoke with a technician at MK Batteries and learned that venting and/or seepage is not uncommon and not a sign of failure.

I have also heard in the distant past and then read recently on a manufacturer's web site that VRLA batteries can and should be equalized.  The parameters are different from an FLA battery.

William Miller




At 09:12 AM 1/6/2012, Larry Crutcher, wrote:
You beat me to that one, Kent. Also, if your VRLA battery is emitting any gas, you've got trouble.

Larry Crutcher
Starlight Solar Power Systems

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to