Jeffrey,

I'll second Jay's suggestion that sealed AGM batteries are the best choice in this circumstance. Presumably this is a grid backup system so the poor endurance of AGMs for cycling applications shouldn't be an issue. If you use a Zephyr power vent horizontal runs shouldn't be problem, but what happens when the power vent fails? It will fail. I've seen the bearings wear out on one and another that failed when insects got into the blades and gummed it up to the point that the motor stalled.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882


On 12/31/2011 6:59 AM, JRQ wrote:
Wrenches,

I'm looking at a potential battery backup system wtih a 200 AH @48V flooded battery bank in the basement electrical room of a 3 story building. There is a window in the electrical room. The batteries will be located about 10' from an outdoor wall. The building is all reinforced concrete, so I can not run a vent pipe vertically from the batteries. Does anyone have a rule of thumb for how much the vent pipes can be angled from the batteries? Would it be more lenient for short sections of pipe (say <2') versus one long angled piece from the batteries? My instinct would be to keep the pipe no more than 45? from plumb.

Or with bending the vent pipe: does anyone have a best-practice rule for the sum of the angles of bends?

Thanks,
Jeffrey Quackenbush
NABCEP Certified PV Installer
Peripatetic Solar Technician
------------------------------------------------------------------------
<mailto:[email protected]>
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to