Drake-     on the tracker installs we've done, the method you describe is 
standard procedure. the exception is that on our very first we used RMC wrapped 
in a continuous layer of anti-corrosion tape to keep the wet concrete from 
attacking the zink coating. 
On all jobs since then we have used only rigid NM stubbed up to just inches 
above the surface of the finished pier. Then we transisitioned to EMT, offset 
and bolted firmly to the steel pipes. 
This process has passed muster when buried conduit penetrated a concrete 
foundation into the new equipment room. A exterior pier should be no different 
from a concrete foundation. Most any commercial electrical contractor in your 
area should be able to detail the process that works in that jurisdiction.
Jim Duncan
North Texas Renewable Energy
817.917.0527
[email protected]
TECL 27398
NABCEP Solar PV
Certified 031310-57
www.ntrei.com
  ----- Original Message ----- 
  From: Drake 
  To: [email protected] 
  Sent: Saturday, December 31, 2011 8:38 AM
  Subject: [RE-wrenches] Pole Mount PVC


  Hello Wrenches,

  With pole mount systems, It looks cleaner and is safer to run the PVC conduit 
down the pole into the concrete, and use a 90 degree elbow to come out through 
the side of the anchor underground.  This way, the pipe is protected from 
mechanical damage, and there is nothing to trip over when adjusting the array 
for seasonal tilt.  

  I was told that some building departments will not allow this.  Has anyone 
had a problem with using this method, either technical or legal?   How do you 
like to route your conduits?

  Thank you,

  Drake 

  Drake Chamberlin         
  ATHENS ELECTRIC LLC
  OH License 44810        
  CO license 3773
  NABCEP Certified PV




------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: [email protected]

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to