Hi Larry,

I am not talking about doing a discharge to 90% DOD,  I was talking about doing 
a discharge to 20% DOD.  Let's say summer folk come up for 1 month a year,  and 
discharge to 20% DOD daily,   then fully recharge with a 2 hour absorb charge 
and then float until the sun goes down. This systems charge controller is set 
to auto EQ every 30 days to stir up the electrolyte,  and all loads are turned 
off when nobody is there.  Let's say there is 4 FLA golf cart batteries and 500 
watts of PV.  Four average sun hours a day.  How long would you expect these 
batteries to last?

Thanks very much,

Jason

Waldron Power and Light Co.
On Jul 13, 2012, at 9:18 AM, <[email protected]> 
<[email protected]> wrote:

> Jason,
> 
> Forcing a lead acid battery to deeply discharge does not increase capacity or 
> life of the battery. It only shortens battery life and may damage the 
> battery. This is one of many battery myths. 
> 
> Larry Crutcher
> Starlight Solar Power Systems
> -------- Original Message --------
> Subject: Re: [RE-wrenches] Battery Experience
> From: Jason Lerner <[email protected]>
> Date: Fri, July 13, 2012 7:28 am
> To: RE-wrenches <[email protected]>
> 
> Hello John,
> 
> This time of year I service off grid summer cabins where people come up once 
> a year for a few weeks.  The batteries in these systems generally do not die 
> from over cycling,  but from over/under watering,  acid stratification, 
> corrosion,  and generally being ignored.  The more savvy customers I will 
> recommend they turn off the PV's when they are there to get a deep discharge 
> in.
> 
> Could you recommend any thing else they could do to lengthen their battery 
> bank lifespan? These systems generally have a small PV charging capability,  
> and float charge 350 days a year. It seems ironic that these systems that 
> really never get used,  and my battery bank at home that gets used (but not 
> abused) and cycled daily, will last the same number of years.
> 
> Thanks very much,
> 
> Jason Lerner
> 
> Waldron Power and Light Co.
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to