Hi Ray,

With no inverter in the system and all the loads turned off do you think the 
batteries are really cycling that much?  Yes your scenario's sound familiar.  
My favorite is a load is left on, the charge controller turns off most, but 
maybe not all the loads with the LVD,  but the battery keeps discharging until 
the battery Voltage gets to low so that Charge controller turns itself off so 
that now no PV charging can occur.

Speaking of battery cell explosions, this spring I had my first.  A customer 
with 8 L16's and 600 watts of PV came to his vacation cabin and found one cell 
had blown up,  with scorch marks on the inside lid of the battery box.  There 
is plenty of ventilation in there,  the owner was meticulous about maintaing 
this 5 year old battery bank.  All cables were bright and tight with no sign of 
corrosion or electrolyte sheen on top of the batteries.  I took it back to the 
manufacturer who shrugged their shoulders and said, "internal short,  it 
happens...."

Have I been lucky not to experience this before?  They made it sound like it 
happens fairly often.

Thanks,

Jason
On Jul 14, 2012, at 10:33 AM, R Ray Walters wrote:

> The batteries in your scenario are actually being cycled daily probably 
> somewhere in the 2 to 5% range.  Looking at a chart for # of cycles vs. DOD, 
> you see the most efficient use of the battery is usually from 20% to 80% DOD, 
>  an FLA battery in perpetual float just doesn't last as long you might think. 
> Depending on the brand of golf car battery, I would give this system a 
> maximum life span of 10 years.
> Maintenance will eventually be the issue; sometime in the battery's life, it 
> will be over charged, left for weeks under charged, or let the water go dry.
> A typical scenario I've seen many times: charge controller fails because of 
> lightning, small load is left on, and the battery gets fully discharged.  
> Since no one is there, it sits for weeks and becomes permanently damaged.  
> Scenario 2 is similar:  a load is left on (light in a closet) fridge or pump 
> stays on and malfunctions,  and the system crashes.
> Scenario 3 no temp compensation, battery gets over charged in the heat, boils 
> its H20 off a couple of cells, the dead cells pull the rest of the bank down 
> in spiraling failure that can actually do damage to the house: acid spills, 
> corrosion, and exploding cells.
> I find my off grid systems that fare the best are well designed full time use 
> with one or two people who are very consistent in their use, and maintenance.
> I've replaced batteries every couple of years on some part time systems, 
> because simple problems are not caught for weeks or months.  I have a couple 
> of higher end part time systems that the owner can monitor and contact us, if 
> for instance the power goes out.  This keeps it from leading to permanent 
> damage.
> 
> Ray Walters
> 
> On Jul 14, 2012, at 8:58 AM, Jason Lerner wrote:
> 
>> Hello John,
>> 
>> Thank you for your helpful explanation.  I wonder if there should be a "six" 
>> life,  that being time.
>> 
>> Lets use the small summer cabin analogy that gets used for one month a year. 
>>  Let's say the system has Four T105 -RE's,  500 watts of PV, 4 average daily 
>> sun hours. They do one discharge/charge cycle down to 20% DOD and then fully 
>> charge again the same day for a 2 hour absorb.  That would be 30 discharge 
>> cycles a year x 8 years = 240 discharge/charge cycles.
>> 
>> If one was to design and instal a proper battery based system using the 
>> guidelines presented in this email thread with plenty of PV for daily 
>> charging,  periodic EQ's, 20% or less DOD, no electrolyte on the battery 
>> tops to cause corrosion, never letting the plates go dry from low 
>> electrolyte level and having them at a cool 60º F year round would you 
>> expect this summer cabin system to last 4000 cycles?  In a perfect world 
>> would that be 4000 cycles ÷ summer cabin 30 discharge/charge cycles a year = 
>> 133 years ??
>> 
>> Of course I am not expecting that,  but am just trying to squeeze the 
>> longest life span possible out of batteries that mostly just sit.
>> 
>> Best,
>> 
>> Jason Lerner
>> 
>> Waldron Power and Light Co.
>> On Jul 13, 2012, at 10:33 AM, John DeBoever wrote:
>> 
>>> Wrenches,
>>>  
>>> Forcing a lead acid battery to cycle for the fun of it reduces its cycle 
>>> life.
>>>  
>>> In a nutshell, lead acid batteries have “five lives”, each varying 
>>> depending their specific intrinsic technology attributes developed by the 
>>> battery OEM:
>>> o   Cycle life
>>> o   Corrosion life
>>> o   Stratification life
>>> o   Shorting life
>>> o   And… Temperature life
>>>  
>>> These lives are all inter-connected and temperature is the one that is the 
>>> most influent to all of them. The interesting part is that all of these “5 
>>> lives” are 90% of the time exacerbated by the system sizing 
>>> (cyclic/non-cyclic, loads, insollation, PV array, battery bank size, wiring 
>>> and power conditioning losses, etc.), the install, the setting points 
>>> commissioning, the maintenance, not to forget the load patterns (perceived 
>>> vs. reality dynamics and growth of the load).  Cycling for cycling does not 
>>> increase the battery life. Adequate cycling based on adequate full recharge 
>>> keep the battery in good health.
>>>  
>>> John
>>>  
>>> John F. DeBoever
>>> Global Technical & Projects Director – Renewable Energy
>>> Trojan Battery Company
>>>  
>>> 12380 Clark Street
>>> Santa Fe Springs, CA 90670
>>> Tel: +1-562-236-3000 Ext. 3139
>>> Cell: +1-845-514-7600 – NY office time zone: USA EST (GMT-5)
>>> Skype: john.f.deboever
>>> Fax: +1-562-236-3239
>>> [email protected]
>>> www.trojanbattery.com
>>>  
>>>  
>>> From: [email protected] 
>>> [mailto:[email protected]] On Behalf Of 
>>> [email protected]
>>> Sent: Friday, July 13, 2012 12:18 PM
>>> To: RE-wrenches
>>> Subject: Re: [RE-wrenches] Battery Experience
>>>  
>>> Jason,
>>>  
>>> Forcing a lead acid battery to deeply discharge does not increase capacity 
>>> or life of the battery. It only shortens battery life and may damage the 
>>> battery. This is one of many battery myths. 
>>>  
>>> Larry Crutcher
>>> Starlight Solar Power Systems
>>> -------- Original Message --------
>>> Subject: Re: [RE-wrenches] Battery Experience
>>> From: Jason Lerner <[email protected]>
>>> Date: Fri, July 13, 2012 7:28 am
>>> To: RE-wrenches <[email protected]>
>>> 
>>> Hello John,
>>>  
>>> This time of year I service off grid summer cabins where people come up 
>>> once a year for a few weeks.  The batteries in these systems generally do 
>>> not die from over cycling,  but from over/under watering,  acid 
>>> stratification, corrosion,  and generally being ignored.  The more savvy 
>>> customers I will recommend they turn off the PV's when they are there to 
>>> get a deep discharge in.
>>>  
>>> Could you recommend any thing else they could do to lengthen their battery 
>>> bank lifespan? These systems generally have a small PV charging capability, 
>>>  and float charge 350 days a year. It seems ironic that these systems that 
>>> really never get used,  and my battery bank at home that gets used (but not 
>>> abused) and cycled daily, will last the same number of years.
>>>  
>>> Thanks very much,
>>>  
>>> Jason Lerner
>>>  
>>> Waldron Power and Light Co.
>>>  
>>> 
>>> This e-mail message and any attachments that accompany it may contain 
>>> information that is confidential, privileged, or protected from disclosure. 
>>> It is intended solely for the use of the individual(s) to whom it was 
>>> intended to be addressed. If you have received this e-mail by mistake, or 
>>> you are not the intended recipient, any reading, disclosure, copying or 
>>> other use of this communication is strictly prohibited. If you have 
>>> received this communication in error, please immediately advise the sender 
>>> at their phone number listed above, or by electronic mail, and also 
>>> permanently delete the original and all copies of this e-mail and any 
>>> attachments from all locations. Thank you. 
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>> 
>>> List Address: [email protected]
>>> 
>>> Options & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>> 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: [email protected]
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to