One big omission, in the otherwise fine Soligent white paper, is that the 60A 
minimum disconnect has to be rated as "Service Equipment". Generally this means 
a "Heavy-Duty" safety switch or Service-rated load center with Main breaker.

I don't see why an AC breaker panel, with a Main breaker, couldn't act as the 
PV system disconnect, as long as it's Service-rated, a minimum of 60A, and the 
utility does not require an external-handle disconnect, lockable in the off 
position. Many utility companies still do.

Brian Teitelbaum
AEE Solar



From: [email protected] 
[mailto:[email protected]] On Behalf Of Jason Szumlanski
Sent: Wednesday, March 12, 2014 2:14 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect

Don't utter the word tap. :)

See:
http://www.soligent.net/documents/HappyLandings_v3.pdf

We usually specify a fusible disconnect for overcurrent protection when 
grouping the PV AC combiner with the main premises disconnect is not practical.


Jason Szumlanski
Fafco Solar




On Wed, Mar 12, 2014 at 1:31 PM, 
<[email protected]<mailto:[email protected]>> wrote:
I am trying to determine whether an AC combiner panel (for multiple inverter 
outputs) with main breaker can be also used as the PV system disconnect?

This is for a line tap situation.  I am accustomed to doing these systems with 
an AC combiner, and separate enclosure for a breaker style, line tap over 
current protection.

Any thoughts/comments would be appreciated.

Thanks,

Kevin

_______________________________________________
List sponsored by Home Power magazine

List Address: 
[email protected]<mailto:[email protected]>

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to