Glenn,
The vast majority of service equipment for residences is rated 10k AIC. Although utilities may say they have some residential services that exceed 10k short circuit availability, it is still pretty rare. Using single phase gear on a 3-phase commercial installation is a different story. Perhaps this is what you were referring to when talking about 10k AIC being too low. I don’t people to get the idea that you have to check the fault current of every PV installation. You should only have to check fault current on a new service. Simply checking the ratings of the exist service equipment at an installation is sufficient to know what the minimum AIC rating of the equipment must be. The utility is not legally allowed to increase the fault current on a service above the service equipment ratings unless it is part of a service upgrade and the service equipment is being replaced. Bill. From: [email protected] [mailto:[email protected]] On Behalf Of Glenn Burt Sent: Wednesday, March 12, 2014 3:13 PM To: RE-wrenches Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect Beware of breakers used as service disconnects. Most in the range suitable for a supply side connections for PV are really branch circuit rated with 10k AIC which is generally too low for the utility fault current they may be exposed to. If you can get a statement from the utility with available fault current at the install site you might sneak one in. If you don't want to go to this trouble, use the rating of the exiting main breaker as a minimum value. Usually 20-25k AIC. _____ From: Brian Teitelbaum <mailto:[email protected]> Sent: 3/12/2014 17:32 To: RE-wrenches <mailto:[email protected]> Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect One big omission, in the otherwise fine Soligent white paper, is that the 60A minimum disconnect has to be rated as “Service Equipment”. Generally this means a “Heavy-Duty” safety switch or Service-rated load center with Main breaker. I don’t see why an AC breaker panel, with a Main breaker, couldn’t act as the PV system disconnect, as long as it’s Service-rated, a minimum of 60A, and the utility does not require an external-handle disconnect, lockable in the off position. Many utility companies still do. Brian Teitelbaum AEE Solar From: [email protected] <mailto:[email protected]> [mailto:[email protected]] On Behalf Of Jason Szumlanski Sent: Wednesday, March 12, 2014 2:14 PM To: RE-wrenches Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect Don't utter the word tap. :) See: http://www.soligent.net/documents/HappyLandings_v3.pdf We usually specify a fusible disconnect for overcurrent protection when grouping the PV AC combiner with the main premises disconnect is not practical. Jason Szumlanski Fafco Solar <https://wisestamp.appspot.com/pixview.gif?p=chrome&v=3.31.0&t=1394658190268&u=eb875d38140ce271> On Wed, Mar 12, 2014 at 1:31 PM, <[email protected] <mailto:[email protected]> > wrote: I am trying to determine whether an AC combiner panel (for multiple inverter outputs) with main breaker can be also used as the PV system disconnect? This is for a line tap situation. I am accustomed to doing these systems with an AC combiner, and separate enclosure for a breaker style, line tap over current protection. Any thoughts/comments would be appreciated. Thanks, Kevin _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] <mailto:[email protected]> Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> Check out participant bios: www.members.re-wrenches.org <http://www.members.re-wrenches.org> --- This email is free from viruses and malware because avast! Antivirus protection is active. http://www.avast.com
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org