Beware of breakers used as service disconnects. Most in the range suitable for 
a supply side connections for PV are really branch circuit rated with 10k AIC 
which is generally too low for the utility fault current they may be exposed to.
If you can get a statement from the utility with available fault current at the 
install site you might sneak one in. If you don't want to go to this trouble, 
use the rating of the exiting main breaker as a minimum value. Usually 20-25k 
AIC.

-----Original Message-----
From: "Brian Teitelbaum" <[email protected]>
Sent: ‎3/‎12/‎2014 17:32
To: "RE-wrenches" <[email protected]>
Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect

One big omission, in the otherwise fine Soligent white paper, is that the 60A 
minimum disconnect has to be rated as "Service Equipment". Generally this means 
a "Heavy-Duty" safety switch or Service-rated load center with Main breaker.

I don't see why an AC breaker panel, with a Main breaker, couldn't act as the 
PV system disconnect, as long as it's Service-rated, a minimum of 60A, and the 
utility does not require an external-handle disconnect, lockable in the off 
position. Many utility companies still do.

Brian Teitelbaum
AEE Solar



From: [email protected] 
[mailto:[email protected]] On Behalf Of Jason Szumlanski
Sent: Wednesday, March 12, 2014 2:14 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect

Don't utter the word tap. :)

See:
http://www.soligent.net/documents/HappyLandings_v3.pdf

We usually specify a fusible disconnect for overcurrent protection when 
grouping the PV AC combiner with the main premises disconnect is not practical.


Jason Szumlanski
Fafco Solar




On Wed, Mar 12, 2014 at 1:31 PM, 
<[email protected]<mailto:[email protected]>> wrote:
I am trying to determine whether an AC combiner panel (for multiple inverter 
outputs) with main breaker can be also used as the PV system disconnect?

This is for a line tap situation.  I am accustomed to doing these systems with 
an AC combiner, and separate enclosure for a breaker style, line tap over 
current protection.

Any thoughts/comments would be appreciated.

Thanks,

Kevin

_______________________________________________
List sponsored by Home Power magazine

List Address: 
[email protected]<mailto:[email protected]>

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to