Bill,

 

I have never seen a main breaker in a residential main load center (say 200A) 
that has a rating of less than 20k AIC. Is there somewhere else in the panel 
that changes this?

 

Glenn

 

From: [email protected] 
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Wednesday, March 12, 2014 7:24 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect

 

Glenn,

 

The vast majority of service equipment for residences is rated 10k AIC. 
Although utilities may say they have some residential services that exceed 10k 
short circuit availability, it is still pretty rare. 

 

Using single phase gear on a 3-phase commercial installation is a different 
story. Perhaps this is what you were referring to when talking about 10k AIC 
being too low. 

 

I don’t people to get the idea that you have to check the fault current of 
every PV installation. You should only have to check fault current on a new 
service. Simply checking the ratings of the exist service equipment at an 
installation is sufficient to know what the minimum AIC rating of the equipment 
must be. The utility is not legally allowed to increase the fault current on a 
service above the service equipment ratings unless it is part of a service 
upgrade and the service equipment is being replaced.

 

Bill.

 

 

From: [email protected] 
[mailto:[email protected]] On Behalf Of Glenn Burt
Sent: Wednesday, March 12, 2014 3:13 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect

 

Beware of breakers used as service disconnects. Most in the range suitable for 
a supply side connections for PV are really branch circuit rated with 10k AIC 
which is generally too low for the utility fault current they may be exposed to.
If you can get a statement from the utility with available fault current at the 
install site you might sneak one in. If you don't want to go to this trouble, 
use the rating of the exiting main breaker as a minimum value. Usually 20-25k 
AIC.

  _____  

From: Brian Teitelbaum <mailto:[email protected]> 
Sent: ‎3/‎12/‎2014 17:32
To: RE-wrenches <mailto:[email protected]> 
Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect

One big omission, in the otherwise fine Soligent white paper, is that the 60A 
minimum disconnect has to be rated as “Service Equipment”. Generally this means 
a “Heavy-Duty” safety switch or Service-rated load center with Main breaker. 

 

I don’t see why an AC breaker panel, with a Main breaker, couldn’t act as the 
PV system disconnect, as long as it’s Service-rated, a minimum of 60A, and the 
utility does not require an external-handle disconnect, lockable in the off 
position. Many utility companies still do.

 

Brian Teitelbaum

AEE Solar

 

 

 

From: [email protected] 
[mailto:[email protected]] On Behalf Of Jason Szumlanski
Sent: Wednesday, March 12, 2014 2:14 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect

 

Don't utter the word tap. :)

 

See:

http://www.soligent.net/documents/HappyLandings_v3.pdf

 

We usually specify a fusible disconnect for overcurrent protection when 
grouping the PV AC combiner with the main premises disconnect is not practical.

 

Jason Szumlanski

Fafco Solar


 

  
<https://wisestamp.appspot.com/pixview.gif?p=chrome&v=3.31.0&t=1394658190268&u=eb875d38140ce271>
 

 

On Wed, Mar 12, 2014 at 1:31 PM, <[email protected]> wrote:

I am trying to determine whether an AC combiner panel (for multiple inverter 
outputs) with main breaker can be also used as the PV system disconnect? 

This is for a line tap situation.  I am accustomed to doing these systems with 
an AC combiner, and separate enclosure for a breaker style, line tap over 
current protection.

Any thoughts/comments would be appreciated.  

Thanks,

Kevin


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 

 

  _____  


 <http://www.avast.com/> 

This email is free from viruses and malware because avast! Antivirus 
<http://www.avast.com/>  protection is active. 

 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to