I get my cable and lugs from Quick Cable but I could not find the fine strand UL listing.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/30/2014 8:09 AM, jay peltz wrote:
Hi ray

As an FYI. Most of the lugs we all use are not "rated" for fine stranded wire.
  Quick cable is the only one I'm aware of that if you use their tool and ends 
says its UL for fine stranded.

I prefer ferrules for those applications vs pin adapters.
(Schneider XW inverter BOS box comes with arctic ultra flex wire with ferrules)

Jay

Peltz power


On Apr 29, 2014, at 10:48 PM, Ray Walters <[email protected]> wrote:

Hi All;

In order to avoid any of my work showing up in someone's slideshow of horrors, 
I'm trying to find the correct way to wire 3 Sunny Islands with Cobra X flex 
cable.
While it doesn't actually mention it in the SMA manual, a call to SMA tech 
support confirmed my suspicions: the DC lugs in the inverter are NOT rated for 
flex or fine stranded cable.
Both SMA and CED recommended I try Grainger's for crimp on adapters.  Grainger 
had no clue, and nothing came up in searches there.
 From a trade show, I have an ILSCO lug book, that shows a crimp on pigtail 
adapter.  It does not mention whether its flex rated though on the crimp side 
of the adapter, as the adapter is used primarily to land over sized cables into 
smaller lugs.  (2/0 to #1, for instance)
The best I've found so far, is NSI, which makes sleeves, that are installed 
around the wire, right in the connection:
http://www.nsiindustries.com/products/electrical/connectors/compression-connectors/copper-compression/fsflex-cable-sleeve.aspx
I also found a Schneider white paper recommending sleeves with their lugs:
http://static.schneider-electric.us/docs/Circuit%20Protection/0515DB0301.pdf

So who has used these sleeves, and where do I get them?
The sleeves seem like a decent compromise, whilst the ILSCO pigtail adapters 
are coming in at $40/ ea...... (ouch)

On the internet, I'm seeing several examples of X flex used directly (no 
adapters) with the Sunny Islands, so are folks just blowing off articles 
690.31(F) and 110.14, that specify the connector be rated for flex cable?
And finally, couldn't SMA use a lug that was flex rated?
For example, Marathon makes Class K rated mechanical Lugs: 
http://www.marathonsp.com/NewRatings.html
I'd use THHN, but I really don't feel good about wiring the Heineman breakers 
with that stiff a wire.  I've cracked breaker cases before......that's why the 
X flex is industry standard for off grid DC.

Thanks for your help,

--
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

_______________________________________________

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to