This may be useful:
http://www.cobrawire.com/lugs/lugs.php?cat=xflex




On 2014/4/30, 14:25, William Miller wrote:
Ray:

Thanks for sharing the research. If you could forward to me of-line an email contact and part number I need to order for 4/0.

Miller Solar

On Apr 30, 2014, at 10:22 AM, Ray Walters <[email protected] <mailto:[email protected]>> wrote:

What I'm finding in my research is that most of the manufacturers are just not keeping up with this requirement, meanwhile the use of fine stranded cable is increasing dramatically. ILSCO, BURNDY, and Quick Cable all barely mention fine strand ratings. I have their catalogs in hand. Even the SMA manual does not mention this issue, I had to call tech support. BTW, there appears to be some big name integrators just using flex cable directly. Meanwhile, I can share a pic of the one lug I torqued down, and didn't like, which lead to all this:
Little copper hairs tearing, or not part of the connection at all.
How did we survive the 90s stuffing welding cable into Heinemann breakers in Trace DC boxes?

Also, when you go into major Electrical suppliers that sell the flex cable, and ask if the connectors are rated for fine stranding, all you get is that "deer in the headlights" stare. I was used to having to figure all this out in the old days of solar, but now that every electrical supplier in town is claiming to be a solar expert/ distributor, I really should be able to just walk in and get the parts I need for a Code compliant installation. If you sell the inverter and the cable, you really should stock the connector.

On another note, the ferrules/ sleeves seem to be the ticket, as confirmed by Schneider. Also they appear to be 40 times cheaper than pin adapters, and don't take up extra room in the wiring compartment. Now I just have to find some TODAY. Ugh...

And like Allan, I lost sleep over this issue last night.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 4/30/2014 10:38 AM, Glenn Burt wrote:
There are many available lugs that are listed for use with finely stranded
conductors - this is not an excuse to not use the proper lugs and required
equipment to ensure a safe and reliable installation (per the NEC).

Thomas & Betts is the manufacturer I use.
Indeed the tool is pricey, however it is  necessary to produce a compliant
installation (per 110.3(B)).

-Glenn

-----Original Message-----
From:[email protected]
[mailto:[email protected]] On Behalf Of jay peltz
Sent: Wednesday, April 30, 2014 10:09 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Flexible stranded Connectors

Hi ray

As an FYI. Most of the lugs we all use are not "rated" for fine stranded
wire.
  Quick cable is the only one I'm aware of that if you use their tool and
ends says its UL for fine stranded.

I prefer ferrules for those applications vs pin adapters.
(Schneider XW inverter BOS box comes with arctic ultra flex wire with
ferrules)

Jay

Peltz power


On Apr 29, 2014, at 10:48 PM, Ray Walters<[email protected]>  wrote:

Hi All;

In order to avoid any of my work showing up in someone's slideshow of
horrors, I'm trying to find the correct way to wire 3 Sunny Islands with
Cobra X flex cable.
While it doesn't actually mention it in the SMA manual, a call to SMA tech
support confirmed my suspicions: the DC lugs in the inverter are NOT rated
for flex or fine stranded cable.
Both SMA and CED recommended I try Grainger's for crimp on adapters.
Grainger had no clue, and nothing came up in searches there.
 From a trade show, I have an ILSCO lug book, that shows a crimp on
pigtail adapter.  It does not mention whether its flex rated though on the
crimp side of the adapter, as the adapter is used primarily to land over
sized cables into smaller lugs.  (2/0 to #1, for instance) The best I've
found so far, is NSI, which makes sleeves, that are installed around the
wire, right in the connection:
http://www.nsiindustries.com/products/electrical/connectors/compressio
n-connectors/copper-compression/fsflex-cable-sleeve.aspx
I also found a Schneider white paper recommending sleeves with their lugs:
http://static.schneider-electric.us/docs/Circuit%20Protection/0515DB03
01.pdf

So who has used these sleeves, and where do I get them?
The sleeves seem like a decent compromise, whilst the ILSCO pigtail
adapters are coming in at $40/ ea...... (ouch)

On the internet, I'm seeing several examples of X flex used directly (no
adapters) with the Sunny Islands, so are folks just blowing off articles
690.31(F) and 110.14, that specify the connector be rated for flex cable?
And finally, couldn't SMA use a lug that was flex rated?
For example, Marathon makes Class K rated mechanical Lugs:
http://www.marathonsp.com/NewRatings.html
I'd use THHN, but I really don't feel good about wiring the Heineman
breakers with that stiff a wire.  I've cracked breaker cases
before......that's why the X flex is industry standard for off grid DC.
Thanks for your help,

--
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

_______________________________________________

_______________________________________________
List sponsored by Home Power magazine

List Address:[email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address:[email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected] <mailto:[email protected]>

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to