Hi Roy,

The FullRiver DC400-6 AGM battery can issue 2000 amps for 5 seconds so he 
should be fine.

Larry

On Jul 2, 2014, at 12:35 PM, Roy Butler <[email protected]> wrote:

I haven't seen anyone mention the battery bank. If I understand correctly, 
there's a single string of sealed
L16 batteries on this inverter. I have my doubts as to whether or not that bank 
can provide the high current
the inverter needs to start this load.
Roy Butler
NABCEP Certified Solar PV Installer®
NYSERDA eligible PV & wind installer
IREC Certified Master Trainer™ for Small Wind Installer
Four Winds Renewable Energy, LLC
8902 Route 46, Arkport, NY 14807
607-324-9747  www.four-winds-energy.com

Join us at the 10th Annual Small Wind Conference
A Gathering of Installers, Manufacturers, Dealers, & Distributors
June 17 and 18, 2014 in Stevens Point, Wisconsin
www.smallwindconference.com

Although no trees were killed in the sending of this message, 
a large number of electrons were terribly inconvenienced.

                
On 7/2/2014 2:10 PM, Jason Szumlanski wrote:
> To further qualify my statements, the inverter will start the pump without 
> issue, but I should echo the warnings by others that if there are other loads 
> present, especially other motor loads that could start ​concurrently, you may 
> experience issues. As long as your customer understands the limitations and 
> possibilities, you may be just fine.
> 
> 
> Jason Szumlanski
> ​ Fafco Solar​ 
> 
> 
> 
> On Wed, Jul 2, 2014 at 11:00 AM, Jason Szumlanski <[email protected]> 
> wrote:
> For what it's worth, I've run a single speed 1.5HP pool pump with a MS4448PAE 
> in a mobile application on a 38.4kWh battery bank (sixteen Rolls S-530's). I 
> have also run a 2.5HP Hayward EcoStar Variable Speed pool pump at full RPM, 
> but that startup current is likely less than you well pump.
> 
> I'm going to guess your 3/4HP well pump will be a breeze to start with this 
> inverter.
> 
> 
> Jason Szumlanski 
> ​ Fafco Solar​ 
> 
> 
> On Wed, Jul 2, 2014 at 10:47 AM, Allan Sindelar <[email protected]> 
> wrote:
> Drake,
> As a normal CYA, I'll always gently let a customer know that this (or any) 
> particular combination of inverter and load sometimes proves incompatible, 
> just in case the unexpected happens. (We once had a MS4448 that would not 
> reliably start and run a condensing boiler; a switch to a different boiler 
> resolved the issue.)
> 
> Having said that note of caution, I wouldn't give it any concern. 3/4 HP and 
> 1 HP well pumps have never been an issue; I would expect 1.5 HP to be easy to 
> run. At 2 HP I'd be asking these questions here. 
> 
> You might check that it's a 3-wire, capacitor-start motor, but nowadays 
> nearly all are. Two-wire pumps (with no control box) can add 50% to the surge.
> 
> The Magnum has a fairly poor voltage regulation response. Sometimes the AC 
> voltage can drop to ~80 VAC momentarily. So you might also caution your 
> customer that the lights may flicker when the pump starts. In our home we 
> know whenever our Kenmore fridge turns on.
> 
> Allan
> 
> Allan Sindelar
> [email protected]
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder (Retired), Positive Energy, Inc.
> 505 780-2738 cell
> 
> 
>  
> On 7/2/2014 8:17 AM, Drake wrote:
>> Hello Wrenches,
>> 
>> We are hoping to use a Magnum PAE 4448 to back up a household that includes 
>> a 3/4 HP deep well pump. There is about 120 feet of vertical rise and about 
>> 1000 feet of horizontal distance. 
>> 
>> I have been told that there is a correlation between the locked rotor 
>> current of a pump and the predictable ability of a specified inverter to 
>> power that pump. 
>> 
>> The plumber who installed the pump left no paperwork and retained no records 
>> of what pump he put in the hole last year. He could only say it was a 3/4 HP 
>> pump. We are therefore unable to obtain the manufacturer's nameplate 
>> specifications.
>> 
>> The Magnum PAE 4448 has a 1 mS surge of 70 A (at 240 V) and a 100 MS surge 
>> of 40 A. According to the NEC Table 430.251(A), a 3/4 HP motor has a locked 
>> rotor current of 41.4 amps at 230 V. 
>> 
>> This inverter can surge at 35.4 A for 5 seconds. The specified battery bank 
>> will be 8 Full River  L-16 AGMs. Can anyone say if:
>> Is there enough information to know if this setup will handle the pump, and 
>> if so, will it?
>> How can an inverter's ability to power a motor or pump be calculated by 
>> knowing its locked rotor current? Which surge periods should be compared to 
>> the locked rotor current?
>> Does the surge current need to equal locked rotor. How long must the 
>> inverter meet its required maximum surge?
>> From experience with Magnums and pumps, does this seem like a good 
>> combination?
>> 
>> Thank you,
>> 
>> Drake 
>> 
>> Drake Chamberlin
>> Athens Electric LLC
>> OH License 44810
>> CO License 3773
>> NABCEP Certified Solar PV 
>> 740-448-7328
>> http://athens-electric.com/ 
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to