We experienced a similar lightning event two years ago that destroyed over a 
dozen modules.  The system was a top of pole ground mount with four rows of 
four poles each, sixteen in total, arranged in a square.  The lightning strike 
occurred 150 feet off the southwest corner of the array, where it hit a utility 
pole.   All the damaged modules were in the front or south most row, and 
concentrated toward the southwest.  The module J-boxes were melted and 
deformed, with burned or exploded diodes.  That was the only sign of damage to 
the system.  The utility lost at least one pole top transformer, and the 
customer some appliances in his nearby farmhouse.  Fortunately the inverters 
were in a barn several hundred feet away.  Being a top of pole mount, the 
system was extensively grounded, with the steel poles at least 4 feet into the 
ground and lines of bare # 6 copper connecting them and multiple ground rods.

Jeff Irish
Hudson Solar
Rhinebeck, NY

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Corey Shalanski
Sent: Tuesday, August 05, 2014 10:03 AM
To: [email protected]
Subject: [BULK] [RE-wrenches] Diode Failure

Wrenches,

We recently were contacted by a customer who reported a lightning strike close 
to his house. His online monitoring revealed that 30 of 35 microinverters 
simultaneously stopped producing power. On initial visit to the jobsite we 
measured Voc on many modules - either 12V or 24V instead of rated 36V. On a 
second visit we discovered that bypass diodes - either 1 or 2 corresponding to 
observed voltage loss - had failed on each of the faulty modules.

My question is: Can anyone support the theory that a nearby lightning flash can 
cause mass bypass diode failure?

--
Corey Shalanski
Joule Energy
New Orleans, LA
[Image removed by sender.]ᐧ
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to