"A diode is a diode." ???????

Not so.

That's like saying a solar panel is a solar panel .. or a tire is a tire.

If you can get the identical part # .. then replace it.  Don't go out and just 
use any diode.

The diodes in PV are commonly a Schottky barrier diode .. designed to minimize 
voltage drop, reduce energy loss .. and operate cooler than "ordinary" diodes 
when they're conducting.  Even something as simple as how they're soldered or 
otherwise attached is also very important, as that aspect is also used to help 
dissipate the heat generated by losses within the diode when it's conducting 
current.  To that point, diodes are often rated to operate up to 175C (nearly 
2X that of boiling water).

Diodes have specific voltage and current ratings.  If you can't replace a diode 
with an identical part .. then you'll have to use as near a match as possible.  
Never go LOWER in ratings .. but if you go too much above .. it may not work 
properly (or long-term reliably) either.

Corey .. contact me off list with the diode part number and I'll see what I can 
do to assist.


Dan


--------------------------------------------
On Mon, 10/20/14, Chris Mason <[email protected]> wrote:

 Subject: Re: [RE-wrenches] Diode Failure
 To: "RE-wrenches" <[email protected]>
 Date: Monday, October 20, 2014, 6:38 PM
Corey,
A diode is a diode. Get an electronics technician to identify the correct part 
and source it.

On Mon, Oct 20, 2014 at 4:51 PM, Corey Shalanski <[email protected]> 
wrote:

    Wrenches,

    Since my previous post (see below) we have recovered the faulty modules and 
are now looking to replace the diodes in order to make them functional again. I 
have had no success sourcing replacement diodes from the original module 
manufacturer, Mage Solar.

    Can anyone recommend a source for replacement diodes?

    --
    Corey Shalanski
    Joule Solar
    New Orleans, LA

    ᐧ
    On Tue, Aug 5, 2014 at 10:27 AM, 
<[email protected]> wrote:


        Message: 10
        Date: Tue, 5 Aug 2014 09:03:09 -0500
        From: Corey Shalanski <[email protected]>
        To: [email protected]
        Subject: [RE-wrenches] Diode Failure
        Message-ID:
                
<ca+smqz1c7kszuqnvzqr0mmux3f2dt6ydum40iseczr2ejrg...@mail.gmail.com>
        Content-Type: text/plain; charset="utf-8"

        Wrenches,

        We recently were contacted by a customer who reported a lightning strike
        close to his house. His online monitoring revealed that 30 of 35
        microinverters simultaneously stopped producing power. On initial visit 
to
        the jobsite we measured Voc on many modules - either 12V or 24V instead 
of
        rated 36V. On a second visit we discovered that bypass diodes - either 
1 or
        2 corresponding to observed voltage loss - had failed on each of the 
faulty
        modules.

        My question is: Can anyone support the theory that a nearby lightning 
flash
        can cause mass bypass diode failure?

        --
        Corey Shalanski
        Joule Energy
        New Orleans, LA

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to