I was going to say to check out the Atkinson gen start unit.

The Classic and other simple voltage sense auxiliary switches can be used to start generators but there isn't necessarily any feedback to tell if the generator actually started or not.

One thing that can be done for feedback is to watch the battery voltage to rise after gen start to see that it actually did start as is being done with the Kid MPPT controller.

Generator stop is pretty much just as important as gen start.
You don't want to run out of fuel unnecessarily.

boB


On 11/8/2014 8:47 AM, Drake wrote:
Hi William,

If the Classic won't work, the Atkinson Generator Start Control Module should do the job. It is basically like the old Gen Wiz.

http://www.atkinsonelectronics.com/manufacturing/products/GSCM.asp

Drake

At 03:45 PM 11/7/2014, you wrote:
Content-Type: multipart/related;
boundary="----=_NextPart_000_00FA_01CFFA88.AA65D390"
Content-Language: en-us

Friend:

I am consulting on an installation without an inverter. We need to start and run a generator to power a Samlex battery charger. We have a Midnite Classic, but in reviewing the manual it is not clear if the unit can be programmed to control a generator sensibly. I have a call into Midnite and am awaiting a reply.

Just starting a generator at a certain low voltage point is inadequate. The generator needs to run until bulk and absorption are accomplished.

We did connect an Outback MX60 to a Mate without an FX once. The menu structure was very different from any manual but we were able to start a generator remotely with the manual relay settings. I just can't remember if it is possible to take advantage of all of the AGS features such as multiple start conditions and the absorption timers with a Mate and an FM60.

Has anyone addressed this scenario?

William


Gradient Cap_mini
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to