Chris: Thanks! More questions. Page 14: I am assuming that the Sonnen system is comprised of the
components and functionality encompassed in the box in the upper
right side of figure 2. And the Outback Radian is the inverter
used for "F" - the "Storage System" inverter? Pages 14, 15, and 29: No info on PV array sizing is provided.
Does the Sonnen design assume that a totally separate grid-tied
inverter system already exists or must be installed if PV charging
is desired? Page 15: The system is AC coupled. When in "Backup Mode" how does
the Sonnen BMS control charging from the external grid-tied PV
inverter system once its battery modules are fully charged and the
house loads are low? Does the Sonnen BMS handle this situation
without disconnecting relays or frequency-shift throttling? Page 15: Is the nomenclature in Figure 2 for the Utility Power Meter "G" and the Consumption Meter "D" reversed? Regards, Gary
On 6/18/16 7:10 PM, Chris Mason wrote:
|
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org