Hello All,

I’m working on a system with 3 Xantrex XW 6048’s that has grid on AC1 and a 20 
kw generator on AC2.  When charging from grid it regulates during an absorption 
charge at 58.2 where it should.  When charging from AC 2 - generator, the 
battery Voltage rises above 62 VDC,  but not every single time.  All the 
settings are correct, EQ is turned off, and if it accidentally got turned on is 
set at the same Voltage as the absorption setting.  Customer has a brand new 33 
kWh AGM battery bank,  that I would rather not fry.  This is a battery backup 
system with no PV.

I have checked all the temperature sensors (they seem good) and tried charging 
with them plugged in,  and with them unplugged and it doesn’t seem to change 
the situation. 

Has anybody else seen this happen before?  Any suggestions?

Thanks very much,

Jason Lerner
Waldron Power and Light Co.
(888) 927-2526

_______________________________________________
List sponsored by Redwood Alliance