Its a pretty small battery bank what do you have the charge rate set to 
10%?100%?  how large is your generator? I will usually start with a lower set 
point, w 3 inverters charging at even 15% thats quite a bit of charging for 
that BB. Make sure your AC input priority is set for AC2 and the Max current is 
what your get can reasonably can handle. but if you are seeing brief 
disconnects then these settings should be checked. Is there a load unknown to 
you after the genre connects say additional loads on the generator feeding 
somewhere else?
I would not swap the AC1 as the settings while are adjustable, there are some 
differences in AC1 & AC2.
T
> On May 4, 2017, at 4:57 PM, Dave Angelini Offgrid Solar 
> <offgridso...@sti.net> wrote:
> 
> On Schneider gear if you program the bat capacity to zero, the unit will
> run the full absorb time. If you had a 1000 AH bank programmed, at 2% of
> the 1000 ah or 20 amps into the battery the unit will go to float. I do
> not see this as your problem though!
> --Dave
> 
>> Hello Kevin,
>> 
>> I have actual battery capacity of 670 ah’s programmed in.  Do you have
>> any theories on why 0 ah’s was helpful??
>> 
>> Swapping AC1 and AC2 is a really good idea.  The only problem is since I
>> put in a micro SD card to the Combox, to do extended logging,  I have not
>> been able to reproduce the problem that was easy to reproduce a month ago.
>> Only thing that has changed is the weather has warmed up.
>> 
>> Schneider tech support has been helpful with suggestions,  but they will
>> not pay to replace the battery bank…..
>> 
>> Jason
>> 
>>> On May 4, 2017, at 9:42 AM, Kevin Pegg <kp...@energyalternatives.ca>
>>> wrote:
>>> 
>>> This is a good one. What battery capacity have you programmed into the
>>> XW system? We have had a few issues, though not this one specifically,
>>> but similar head-scratchers that were resolved by setting the battery
>>> capacity to 0 Ah.
>>> 
>>> Have you tried swapping AC1 and AC2 and does the problem follow the
>>> source or the input?
>>> 
>>> I recently had an odd issue with generator automation on AC1 on an XW+
>>> and Schneider tech support was helpful in replicating the issue in their
>>> lab and issuing a fix. Might be worth engaging them if you haven't
>>> already.
>>> 
>>> Kevin
>>> 
>>> -----Original Message-----
>>> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
>>> Behalf Of Jason Lerner
>>> Sent: May-03-17 3:18 PM
>>> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
>>> Subject: [RE-wrenches] Xantrex XW 6048A unregulated during charging
>>> 
>>> Hello All,
>>> 
>>> I’m working on a system with 3 Xantrex XW 6048’s that has grid on
>>> AC1 and a 20 kw generator on AC2.  When charging from grid it regulates
>>> during an absorption charge at 58.2 where it should.  When charging from
>>> AC 2 - generator, the battery Voltage rises above 62 VDC,  but not every
>>> single time.  All the settings are correct, EQ is turned off, and if it
>>> accidentally got turned on is set at the same Voltage as the absorption
>>> setting.  Customer has a brand new 33 kWh AGM battery bank,  that I
>>> would rather not fry.  This is a battery backup system with no PV.
>>> 
>>> I have checked all the temperature sensors (they seem good) and tried
>>> charging with them plugged in,  and with them unplugged and it doesn’t
>>> seem to change the situation.
>>> 
>>> Has anybody else seen this happen before?  Any suggestions?
>>> 
>>> Thanks very much,
>>> 
>>> Jason Lerner
>>> Waldron Power and Light Co.
>>> (888) 927-2526
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
>> 
> 
> 
> Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/
> e-mail  offgridso...@sti.net
> text 209 813 0060
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

> t...@swnl.net 
> <blocked::mailto:t...@swnl.net%22%20%5Co%20%22blocked::mailto:t...@swnl.net>  
>              www.SWNL.net 
> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                      
>         
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to