I remember seeing something similar, but can't remember fix.. Might
   have been low / wrong oil.. Maybe bad sensor.. Loose connection? maybe
   bad board.. Might want to check fuses.. Could be a sticky reg.. might
   be out of gas.. I have it on good authority 'The knees are not always
   the first to go'.. Good Luck.

   db

   Dan Brown
   Foxfire Energy Corp.
   Renewable Energy Systems
   (802)-483-2564
   [1]www.Foxfire-Energy.com
   NABCEP #092907-44

   -------- Original Message --------
   Subject: Re: [RE-wrenches] GENERAC EcoGen 6kw problem
   From: Ray <[2][email protected]>
   Date: Mon, January 08, 2018 10:54 pm
   To: [3][email protected]
   I recently had a frustrating generator trouble shoot that was similar,
   turned out to be a dirty air filter of all things.  Easy fix, but took
   a
   couple of hours to come to that conclusion.......
   Ray
   Remote Solar
   On 1/8/2018 5:38 PM, David Palumbo wrote:
   > Can the programming change on its own? I shut it off after it ran two
   days ago at my neighbors and no one touched it before I started it
   today. Neighbors are away and no footprints in new snow.
   > Dave
   >
   > Sent from Mail for Windows 10
   >
   > From: [4][email protected]
   > Sent: Monday, January 8, 2018 7:30 PM
   > To: RE-wrenches
   > Subject: Re: [RE-wrenches] GENERAC EcoGen 6kw problem
   >
   > Check to see if it’s programming matches its wired and expected
   voltage output configuration.
   >
   > Sent from my iPhone
   >
   >> On Jan 8, 2018, at 6:13 PM, David Palumbo <[5][email protected]>
   wrote:
   >>
   >> I am troubleshooting a 6kw EcoGen LP gas generator in my
   neighborhood that starts quickly
   >> • but immediately shuts down with an “Under Voltage” shutdown alarm
   >> • I can clear shutdown alarm and restart with same result. I tried
   this a few times with same result. One of the start attempts included a
   back fire before shutting down.
   >> • Generator was recently run successfully for a few hours during a
   cold snap. Started after several attempts at -10 F.
   >> • According to the EcoGen manual this Under Voltage alarm is
   triggered “If the generator voltage falls below 85% of nominal for more
   than 15 seconds”. This definitely isn’t happening as the generator
   starts as usual but shuts down within one or two seconds.
   >> I will check for fouled spark plugs tomorrow. Anything else that
   might be the problem?
   >>
   >> David Palumbo
   >> Independent Power LLC
   >> Hyde Park, VT
   >> 802-371-8678 voice or text
   >>
   >> Sent from Mail for Windows 10
   >>
   >> _______________________________________________
   >> List sponsored by Redwood Alliance
   >>
   >> List Address: [6][email protected]
   >>
   >> Change listserver email address & settings:
   >>
   [7]http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
   >>
   >> List-Archive:
   [8]http://www.mail-archive.com/[email protected]/mailli
   st.html
   >>
   >> List rules & etiquette:
   >> [9]www.re-wrenches.org/etiquette.htm
   >>
   >> Check out or update participant bios:
   >> [10]www.members.re-wrenches.org
   >>
   > _______________________________________________
   > List sponsored by Redwood Alliance
   >
   > List Address: [11][email protected]
   >
   > Change listserver email address & settings:
   >
   [12]http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.or
   g
   >
   > List-Archive:
   [13]http://www.mail-archive.com/[email protected]/maill
   ist.html
   >
   > List rules & etiquette:
   > [14]www.re-wrenches.org/etiquette.htm
   >
   > Check out or update participant bios:
   > [15]www.members.re-wrenches.org
   >
   >
   > _______________________________________________
   > List sponsored by Redwood Alliance
   >
   > List Address: [16][email protected]
   >
   > Change listserver email address & settings:
   >
   [17]http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.or
   g
   >
   > List-Archive:
   [18]http://www.mail-archive.com/[email protected]/maill
   ist.html
   >
   > List rules & etiquette:
   > [19]www.re-wrenches.org/etiquette.htm
   >
   > Check out or update participant bios:
   > [20]www.members.re-wrenches.org
   >
   _______________________________________________
   List sponsored by Redwood Alliance
   List Address: [21][email protected]
   Change listserver email address & settings:
   [22]http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.or
   g
   List-Archive:
   [23]http://www.mail-archive.com/[email protected]/maill
   ist.html
   List rules & etiquette:
   [24]www.re-wrenches.org/etiquette.htm
   Check out or update participant bios:
   [25]www.members.re-wrenches.org

References

   1. http://www.Foxfire-Energy.com/
   2. mailto:[email protected]
   3. mailto:[email protected]
   4. mailto:[email protected]
   5. mailto:[email protected]
   6. mailto:[email protected]
   7. http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
   8. 
http://www.mail-archive.com/[email protected]/maillist.html
   9. http://www.re-wrenches.org/etiquette.htm
  10. http://www.members.re-wrenches.org/
  11. mailto:[email protected]
  12. http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  13. 
http://www.mail-archive.com/[email protected]/maillist.html
  14. http://www.re-wrenches.org/etiquette.htm
  15. http://www.members.re-wrenches.org/
  16. mailto:[email protected]
  17. http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  18. 
http://www.mail-archive.com/[email protected]/maillist.html
  19. http://www.re-wrenches.org/etiquette.htm
  20. http://www.members.re-wrenches.org/
  21. mailto:[email protected]
  22. http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  23. 
http://www.mail-archive.com/[email protected]/maillist.html
  24. http://www.re-wrenches.org/etiquette.htm
  25. http://www.members.re-wrenches.org/
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to