Wrenches We have been doing testing on the Blue Ion over the last several months, we have been using PV, back up grid connected charger, we have CT's on DC in, PV in, Charger in, and Load out, some days we push to three cycles a day, other days 1/2 cycle. The Blue Ion BMU has done well keeping everything in control including a relay for the charger. Eguage has done all the monitoring and has some impressive data. Jerry
On Feb 20, 2018 6:02 AM, "Kirpal" <[email protected]> wrote: > Larry....yes those are big claims (8000 cyclces at 100% DOD!) No I don't > have the data showing that, nor have I seen it. But the marketing has to > be accurate right?! We have installed a few systems with a few more on the > books including one at our office. Will be interesting to see if the real > world matches the lab tests....I don't have a copy of their warranty but it > is for 15 years and does allow for some degradation of capacity, 70% > remaining after 15 years. Pretty robust for a battery warranty! From what > I have seen they are a strong off grid option. Could be one of the last > battery banks some of our customers ever buy. The visibility into cycle > count and remaining capacity is refreshing after using various amp hour > meters which tend to wander in accuracy over time. I am looking forward to > the migration away from Lead Acid in the years ahead! > > > Sunny Regards, > Kirpal Khalsa > Oregon LRT#25 > NABCEP Certified PV Installation Professional > Oregon Solarworks LLC > www.oregonsolarworks.com > 541-299-0402 <(541)%20299-0402> > > On Mon, Feb 19, 2018 at 4:08 PM, Starlight Solar Power Systems < > [email protected]> wrote: > >> Hi Kirpal, >> >> “...8000 cycles (20+ years of daily cycling!!) to 100 depth of >> discharge…” >> I saw that on their website but there is no substantiating data from real >> cycle life tests. When Sony introduced this battery, they claimed 2000 >> cycles at 80% DoD. For such an extraordinary claim, there must be a catch. >> Do you have any information about testing or a copy of their warranty? >> >> >> Larry Crutcher >> Starlight Solar Power Systems >> >> >> >> >> >> >> On Feb 19, 2018, at 4:10 PM, Kirpal <[email protected]> wrote: >> >> Blue Planet - Lithium Iron Phosphate batteries are a good option for off >> grid and work very well with the Outback Radian inverters. They are rated >> at 8000 cycles (20+ years of daily cycling!!) to 100 depth of discharge and >> can be monitored remotely. The batteries , like in the Sonnen system are >> made by Sony. >> The company was just down in PR doing some installs and had some very >> good feedback from local installers. >> One more option for the tool bag. >> Also, Outback just released a white paper on AC coupling using a solid >> state relay into the Radian. So they are now providing some guidance on >> this as of just recently. I still prefer DC coupling with grid tied mode >> when the grid does come back around. >> >> >> >> Sunny Regards, >> Kirpal Khalsa >> Oregon LRT#25 >> NABCEP Certified PV Installation Professional >> Oregon Solarworks LLC >> www.oregonsolarworks.com >> 541-299-0402 <(541)%20299-0402> >> >> On Mon, Feb 19, 2018 at 11:14 AM, Ray <[email protected]> wrote: >> >>> Greetings Wrenches; >>> >>> We are designing several systems for Puerto Rico, and while these will >>> eventually could be grid tied once the grid returns, they will need to >>> operate reliably in off grid mode possibly for a year or more. What is >>> everyone's experiences with the Storedge and LG setup? I've worked with >>> the regular Solaredge GT system and was quite impressed, but I've heard the >>> Storedge is not a good off grid option. What are the issues, and has >>> anyone used the Storedge in longer term outages? >>> >>> Right now we are designing some smaller systems that will use Magnum >>> inverters with 24v and 48 v Li+ batteries from other manufacturers, like >>> Simpliphi and LiFe Blue. ( No GT, Backup only) These are lower cost and >>> allow us to use more traditional off grid designs, but also have limited >>> charge and discharge current. In order to make Li+ cost effective, we have >>> had to reduce the storage size in half compared to lead acid. We feel this >>> is justifiable considering Li+'s ability to be discharged to 100%, its >>> voltage stability, and its higher efficiency. >>> >>> All feed back is welcome, as we venture into less well charted >>> territory. We just don't want to set up systems that are going to not be >>> functional in 5 to 8 years because of inferior AGM lead acid batteries. We >>> use HUP batteries for most larger off grid systems, but these are not >>> feasible because of their size and maintenance requirements. >>> >>> Thanks, >>> >>> Ray Walters >>> >>> Remote Solar >>> >>> _______________________________________________ >>> List sponsored by Redwood Alliance >>> >>> List Address: [email protected] >>> >>> Change listserver email address & settings: >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>> >>> List-Archive: http://www.mail-archive.com/re >>> [email protected]/maillist.html >>> >>> List rules & etiquette: >>> www.re-wrenches.org/etiquette.htm >>> >>> Check out or update participant bios: >>> www.members.re-wrenches.org >>> >>> >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> List Address: [email protected] >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: http://www.mail-archive.com/re >> [email protected]/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> >> >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> List Address: [email protected] >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: http://www.mail-archive.com/re >> [email protected]/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> >> > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: http://www.mail-archive.com/[email protected]. > org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > >
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org

