Midnite has some string level and module level 690.12 disconnects that wire in like an optimizer or micro inverter, so those should be able to meet the 2019 requirements.  However beware:  they as of yet still don't have a reasonable disconnect system to disconnect the charge controller which has capacitors that back feed the PV line for up to 90 seconds.  They have a DC GFI breaker with remote trip capability but it takes 4 spaces, so with multiple charge controllers it turns into a wiring mess really fast.

I actually wired in some 60 amp rated diodes on one system to get it to pass inspection; what a joke, going back to 1980s equipment to pass 2017 code.    690.12 is an absolute nightmare for small off grid.  There really should be some exemptions for small arrays (under 3 kW) and under 100 vdc.  Fire fighters are not going to get there till the structure is down anyway,  Response times are up to an hour for remote locations with volunteer fire departments.  Its not like in town at all;  no one is going to go on the roof on an off grid fire.

On the flip side, there are real dangers created by nuisance tripping of 690.12 equipment.  Again, on grid it's a mere inconvenience, but off grid it could mean spoiled food, frozen water lines, shut down heating systems in subzero temperatures, and for the elderly: loss of their breathing machines.  I've already had a 74 year old customer climbing on their roof multiple times to reset the Rapid shutdown equipment after nuisance trips. Are we going to wait until we get someone killed in the name of "Safety" before we fix this?

Ray Walters
Remote Solar
303 505-8760

On 7/6/18 9:55 AM, cwarfel wrote:

I am wondering about the experience installers have with a DC coupled multimode system design that will comply after January 1 with what I feel is the biggest mistake/poorly guided part of NEC 2017 690, and that is 690.12. We are installing two Outback systems with the remote controlled combiner and even that won't comply after January 1 unless we parallel more subarrays (There's safety for you, lower voltage-higher amperage!). Thanks for any insight.

Chris




--

         Christopher Warfel, PE
       ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
               (401)466-8978

EEI logo <http://entech-engineering.com>


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to