Thanks Ray, I am sure the moderator will let me know if this is off
topic, but I would be willing to help organize a petition drive to
repeal this part of the NEC and because there are good reasons. Not
because it's "inconvenient". Long time manufacturers, who historically
produced safe and high quality product(s) are being harmed by this
language, which in turn, benefited others. Safety is not necessarily
increased. I feel CMP 4 got hijacked focusing on this issue. There has
been good reorganization and integration of 690 with other Articles, but
RS is not reflective of this effort. Just the labeling requirements show
that.
There is a lot of focus on resiliency and the NEC increased the cost and
didnot improvethe safety of DC coupled multimode systems. So instead of
incorporating the roof resource that could be used to meet resiliency
goals, we are taking roofs out of some design considerations, and
increasing the costs for the other options.
Chris
On 7/6/2018 1:32 PM, Ray wrote:
Midnite has some string level and module level 690.12 disconnects that
wire in like an optimizer or micro inverter, so those should be able
to meet the 2019 requirements. However beware: they as of yet still
don't have a reasonable disconnect system to disconnect the charge
controller which has capacitors that back feed the PV line for up to
90 seconds. They have a DC GFI breaker with remote trip capability
but it takes 4 spaces, so with multiple charge controllers it turns
into a wiring mess really fast.
I actually wired in some 60 amp rated diodes on one system to get it
to pass inspection; what a joke, going back to 1980s equipment to pass
2017 code. 690.12 is an absolute nightmare for small off grid.
There really should be some exemptions for small arrays (under 3 kW)
and under 100 vdc. Fire fighters are not going to get there till the
structure is down anyway, Response times are up to an hour for remote
locations with volunteer fire departments. Its not like in town at
all; no one is going to go on the roof on an off grid fire.
On the flip side, there are real dangers created by nuisance tripping
of 690.12 equipment. Again, on grid it's a mere inconvenience, but
off grid it could mean spoiled food, frozen water lines, shut down
heating systems in subzero temperatures, and for the elderly: loss of
their breathing machines. I've already had a 74 year old customer
climbing on their roof multiple times to reset the Rapid shutdown
equipment after nuisance trips. Are we going to wait until we get
someone killed in the name of "Safety" before we fix this?
Ray Walters
Remote Solar
303 505-8760
On 7/6/18 9:55 AM, cwarfel wrote:
I am wondering about the experience installers have with a DC coupled
multimode system design that will comply after January 1 with what I
feel is the biggest mistake/poorly guided part of NEC 2017 690, and
that is 690.12. We are installing two Outback systems with the remote
controlled combiner and even that won't comply after January 1 unless
we parallel more subarrays (There's safety for you, lower
voltage-higher amperage!). Thanks for any insight.
Chris
--
Christopher Warfel, PE
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
(401)466-8978
EEI logo <http://entech-engineering.com>
_______________________________________________
List sponsored by Redwood Alliance
List Address:[email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
--
Christopher Warfel, PE
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
(401)466-8978
EEI logo <http://entech-engineering.com>
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org