The issue I first raised was within the array boundary. It was very helpful that it was clarified that battery conductors are not PV circuits. This still leaves the problem of dc coupled multimode inverters on a roof having to limit the voltage to 80 or less.  It really needs to be changed toat least 150vdc.  A tremendous national resource in dc couple potential has been written out of existence.

On 7/6/2018 4:57 PM, Rebekah Hren wrote:
I believe there was a big improvement for off-grid systems as relates to RS in the 2017 NEC - the diagrams in 690.1(b) all show the PV system disconnect clearly now.  If you check out the diagrams you can see that energy storage/battery circuits, including the battery-based inverter whether AC or DC coupled, are outside the PV system boundary, thus not PV system circuits, thus not subject to RS.

Also, the NEC 2020 1st draft report has been published <https://downloads.nfpa.org/codes-and-standards/all-codes-and-standards/list-of-codes-and-standards/detail?code=70&tab=nextedition>, so get your comments submitted!

Rebekah Hren
Member, NEC CMP-4

On Fri, Jul 6, 2018 at 2:22 PM Dan Fink <[email protected] <mailto:[email protected]>> wrote:

    I agree with you, Ray, as a purely off-grid solar installer and
    troubleshooter. I think all that was accomplished in NEC 2017 on
    this issue is that non-habitable structures, like the common
    off-grid 'power shed' don't need 690.12 RS anymore.

    Dan Fink
    Professor of Solar Energy Technology, Ecotech Institute
    IREC Certified Instructor™ for:
    ~ PV Installation Professional
    ~ Small Wind Installer
    Executive Director, Buckville Energy
    NABCEP Registered Continuing Education Providers™
    NABCEP Associate

    970.672.4342


    On Fri, Jul 6, 2018 at 11:32 AM, Ray <[email protected]
    <mailto:[email protected]>> wrote:

        Midnite has some string level and module level 690.12
        disconnects that wire in like an optimizer or micro inverter,
        so those should be able to meet the 2019 requirements. 
        However beware:  they as of yet still don't have a reasonable
        disconnect system to disconnect the charge controller which
        has capacitors that back feed the PV line for up to 90
        seconds.  They have a DC GFI breaker with remote trip
        capability but it takes 4 spaces, so with multiple charge
        controllers it turns into a wiring mess really fast.

        I actually wired in some 60 amp rated diodes on one system to
        get it to pass inspection; what a joke, going back to 1980s
        equipment to pass 2017 code. 690.12 is an absolute nightmare
        for small off grid. There really should be some exemptions for
        small arrays (under 3 kW) and under 100 vdc.  Fire fighters
        are not going to get there till the structure is down anyway, 
        Response times are up to an hour for remote locations with
        volunteer fire departments.  Its not like in town at all;  no
        one is going to go on the roof on an off grid fire.

        On the flip side, there are real dangers created by nuisance
        tripping of 690.12 equipment.  Again, on grid it's a mere
        inconvenience, but off grid it could mean spoiled food, frozen
        water lines, shut down heating systems in subzero
        temperatures, and for the elderly: loss of their breathing
        machines. I've already had a 74 year old customer climbing on
        their roof multiple times to reset the Rapid shutdown
        equipment after nuisance trips.  Are we going to wait until we
        get someone killed in the name of "Safety" before we fix this?

        Ray Walters
        Remote Solar
        303 505-8760

        On 7/6/18 9:55 AM, cwarfel wrote:

        I am wondering about the experience installers have with a DC
        coupled multimode system design that will comply after
        January 1 with what I feel is the biggest mistake/poorly
        guided part of NEC 2017 690, and that is 690.12. We are
        installing two Outback systems with the remote controlled
        combiner and even that won't comply after January 1 unless we
        parallel more subarrays (There's safety for you, lower
        voltage-higher amperage!). Thanks for any insight.

        Chris




--
        Christopher Warfel, PE
               ENTECH Engineering, Inc.
        PO Box 871, Block Island, RI 02807
                       (401)466-8978

        EEI logo <http://entech-engineering.com>


        _______________________________________________
        List sponsored by Redwood Alliance

        List Address:[email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>



        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>



    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



--
Tel: 336.266.8800
NABCEP Certified Solar PV Installation Professional™ 091209-85
NC Licensed Electrical Contractor


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


--

         Christopher Warfel, PE
       ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
               (401)466-8978

EEI logo <http://entech-engineering.com>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to