Return amps at 0 is physically impossible I think. The lowest Return amps I have ever seen acknowledged by a charge controller on a 24-volt set was 3-4 amps on a new set of batteries. Older sets 6-8 amps.
I was trying to see how low you could go before it would stop Bulk. 29.8 for 6 hours? was cooking them plates& boiling off electrolyte. These batteries must have been so hot. To Float my 48-volt HUP set takes about 250-300 watts with no load. 5.21-6.25 amps. ---------------------------------------------------------------------------- Dana Orzel Great Solar Works, Inc. C - 208.721.7003 [email protected] Idaho Contractor - # 028765 Idaho PV # 028374 NABCEP # 051112-136 www.solarwork.biz <http://www.solarwork.biz> "Responsible Technologies for Responsible People since 1988" P Please consider the environment before printing this email. From: RE-wrenches <[email protected]> On Behalf Of Mac Lewis Sent: Tuesday, September 11, 2018 6:44 PM To: RE-wrenches <[email protected]> Subject: [RE-wrenches] Trojan L16RE-2V set-points Hello wrenches, I inspected a system that another company had installed. It had single string of 12 x Trojan L16RE-2V batteries about 2 years old. They had experienced a battery melt-down. It looks as though the meltdown had occurred internally, not from a bad connection. The system was dual stack Outback VFXR-3524A inverters (to be precise one was a sealed unit). The set-points were as follows: Absorb Voltage was 29.8V Absorb Time was 6.0 hours Float Voltage was 27.0V Rebulk Voltage was 27.0V End Amps was 0A These settings extended similarly to 2 x FM80 charge controllers. I was able to jumper the melted battery and get her power in 15 minutes. Her installer had left her without power for 2 weeks. My clients will kill me if that happened! Anyway, I believe these set-points are way out of whack and too aggressive. The voltage is OK (Trojan recommends ~29.6V for this) but the Absorb time seems way too long, Rebulk is too high and end amps isn't helping. However, Im not finding a definitive article from Trojan that describes typical Absorb times or even how to adjust towards a good Absorb Time, based on specific gravity measurements or amperage absorption. My diagnosis is that these batteries have been cooked over the past 2 years. In the electrolyte, there is noticeable "floaties". The client said that the original installer had accused her of not using distilled water, but I don't believe that would cause her symptoms. I believe the floaties are plate material. I'd be interested in wrenches opinions familiar with these batteries if these are appropriate settings for a low energy user. I will attempt to get through to Trojan as well. Thanks in advance -- Mac Lewis "Yo solo sé que no sé nada." -Sócrates
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org