Might want to confirm that the FNDC Relay is off and just the AGS relay is set 
from the Mate menu.

Seems I went through this one time before and excellent Outback support quickly 
surmised the issue for me.

Scot Arey
Solar CenTex

 

From: RE-wrenches <[email protected]> On Behalf Of Mac 
Lewis
Sent: Friday, April 19, 2019 12:27 PM
To: RE-wrenches <[email protected]>
Subject: [RE-wrenches] Operating Voltages Outback RE High Capacity Battery

 

Hello Wrenches,

 

We recently inherited an Outback system that I've been keeping an eye on via 
Optics.  Its a dual stack 3648 VFXR, with about 4kW of PV with a single string 
of EnergyCell 1100RE battery bank (reported to be ~6 months old) ~.46 kWh at 
C20.

 

I have been observing how the system functions and how the voltage behaves.  We 
keep getting 2 minute voltage starts on the generator in the middle of the 
night that don't seem necessary judging from how much energy has been used from 
the battery bank.  I am hesitant to tweak anything because these battery 
set-points are a bit different than I'm used to.

 

As per Outback:

Absorb Voltage is 55.6V for 2 hours

Float Voltage is 54.0V

 

I've slowly been dropping the 2 minute start voltage to see if there is a 
bottom, but I'm hesitant to take it much lower (maybe I should). 

2 minute start voltage: 44.8 V.

 

 

The system easily charges the battery bank to 100% (and easily reached the 2 hr 
absorb time) every day.  The flexnet DC is correctly set up and calibrated.

 

The load on the system is pretty consistent.  They use between 400 and 600W 
throughout the night.

 

An average night, they may use about 6 kWh before the voltage sags below the 2 
minute start voltage and it starts the generator.

 

Just curious if our 2 minute voltage needs to be dropped or if these batteries 
are degraded.  What corrective changes can I make to get better performance?

 

I have and will call Outback about this, but I'd like other perspectives as 
well.

 

Thanks as always for your expertise


 

-- 

 

 

 

Mac Lewis

"Yo solo sé que no sé nada." -Sócrates

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to