Midnite Solar has their SOB system that attaches inline with the
modules. It can do both String level and module level shutdown. We've
used it off grid with success. The biggest issue is it is not
compatible with most charge controllers, except Magnum's PT 100 for some
reason. We used the PT 100, used one pole of a 3 pole DC disconnect for
the "ON" signal, and all worked fine. No nuisance tripping or other
issues for over a year. We did not bother with controlled breakers,
etc at the charge controller, and certainly not the inverter.
As is clear in Figure 690.1(b) Note (2) /The PV system disconnect...
separates the PV system from all other systems. /This means that we
label the external DC disconnect as /PV Disconnect, /and the voltage
requirements of 690.12 only apply up to that PV disconnect. Articles
445 Generators, 480 Batteries, 705 Interconnected Systems, 706 Storage
Systems, and 710 Stand Alone Systems, all apply after the PV disconnect.
Ray Walters
Remote Solar
303 505-8760
On 9/27/19 11:23 AM, Lorenzo Ortiz wrote:
Wrenches,
Are any of you looking ahead at solutions for module level rapid
shutdown for off grid? Here in CA it's being implemented next year (at
least in my area) and I haven't found any reliable, proven,
*cost-effective* products yet.
I know Tigo has some sort of inline component but haven't heard a lot
about it.
Any input is appreciated.
Thanks
--
__
Loren Ortiz
Technical PV Design Specialist - Commercial/Residential/Off-Grid
[email protected] <mailto:[email protected]> californiasolarco.com
<http://californiasolarco.com>
*Main:530-274-3671 ext: 311 ****Fax:530-274-7518*
**
<https://californiasolarco.com/referral_form/>
*Showroom located at: 149 E Main St. Grass Valley, CA 95945*
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org