Just another reminder that one should most always do what the AHJ or
inspector wants. When they are done you can do what is sensible and very
often safer. We have a new inspector here who is about 24 years old who is
really good. 

Over the years it has been interesting/amusing to watch the
learning curve. 
Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail [email protected]
[2]
text 209 813 0060

On Sat, 28 Sep 2019 01:56:56 +0000, "Jason Fisher
(STC)"  wrote:        Just a reminder to everyone struggling with this
issue that only building-attached circuits energized by PV sources require
RSD. So ground mounts generally don't, or at least would only require a
disconnect at the building if sending dc circuits into buildings.    Energy
Storage is covered under article 706 in 2017 and does not require any
shutdown, just sensible disconnection requirements.    Jason Fisher     

-------------------------
 FROM: RE-wrenches  on behalf of Chris Sparadeo

 SENT: Friday, September 27, 2019 5:00 PM
 TO: RE-wrenches
 SUBJECT: Re:
[RE-wrenches] Module-Level Shutdown for off grid systems     For AC coupled
battery based systems it's a pretty easy solution. Any run of the mill
module level RSD compliant grid tied inverter system can work. Obviously,
there are major advantages to DC coupling and this is were it gets tricky.
Outback has a nice string level RSD option with the ICS, but I haven't
found a comparable solution for other products. This seems like a great
opportunity for a company like MidNite to create a solution.  
  On Fri,
Sep 27, 2019 at 6:59 PM Chris Sparadeo  wrote:    For AC coupled battery
based systems it's a pretty easy solution. Any run of the mill module level
RSD compliant grid tied inverter system can work. Obviously, there are
major advantages to DC coupling and this is were it gets tricky. Outback
has a nice string level RSD option with the ICS, but I haven't found a
comparable solution for other products. This seems like a great opportunity
for a company like MidNite to create a solution.     
  On Fri, Sep 27,
2019 at 6:21 PM Glenn Burt  wrote:    The difference in topologies is that
when the Tigo devices are used with an inverter driving the control is that
it is relying on the Sunspec Alliance standard to be implemented correctly
between the inverter manufacturer and Tigo. When using the Tigo devices at
the modules and the Togo RSS box for control, the inverter is not involved
and it removes a layer of possible incompatibility and finger pointing if
things go sideways.   We have been told of such hiccups by our distributor,
and they are pushing the IMO Fire raptor solution. Unfortunately they sell
the SMA branded Tigo devices so have no feedback on their use with the RSS
controller, only with the SMA inverter control of the rooftop devices. I
have attended a couple of Tigo trainings, and the all Togo option looks
straightforward. We have quoted their use a couple of times now, but have
not yet done an install.    -Glenn Sent from my 'smart'phone, so please
excuse typos and spelling errors.       ------ Original message------ FROM:
Jerry Shafer DATE: Fri, Sep 27, 2019 1:40 PM TO: RE-wrenches; CC: 
SUBJECT:Re: [RE-wrenches] Module-Level Shutdown for off grid systems   
Wrenches Yes l am looking at the Tigo, they work with SMA and outback, 
Jerry  
  On Fri, Sep 27, 2019, 10:24 AM Lorenzo Ortiz  wrote:  Wrenches,  
Are any of you looking ahead at solutions for module level rapid shutdown
for off grid? Here in CA it's being implemented next year (at least in my
area) and I haven't found any reliable, proven, COST-EFFECTIVE products
yet.  I know Tigo has some sort of inline component but haven't heard a lot
about it.   Any input is appreciated.   Thanks    -- 
                     
                 Loren Ortiz  Technical PV Design Specialist -
Commercial/Residential/Off-Grid 
   [email protected] [6]
californiasolarco.com [7] 
  MAIN:  EXT: 311 FAX:   

                     
              < /div>              
 SHOWROOM LOCATED AT: 149 E MAIN ST.
GRASS VALLEY, CA 95945 _______________________________________________

List sponsored by Redwood Alliance

 List Address: 
[email protected] [9]

 Change listserver email address &
settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [10]


List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html
[11]

 List rules & etiquette:
 www.re-wrenches.org/etiquette.htm [12]


Check out or update participant bios:
 www.members.re-wrenches.org [13]
   
 _______________________________________________
 List sponsored by
Redwood Alliance

 List Address:  [email protected] [14]


Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [15]


List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html
[16]

 List rules ">_Chris Sparadeo_ 

_NABCEP CERTIFIED PV INSTALLATION
PROFESSIONAL # 042919-015652_

Catamount Solar, LLC 

4 Randolph Ave.,
Randolph, VT 05060 

C_(802) 369-4458 

O_(802) 728-3600


www.CatamountSolar.com [19] 

         -- 
      Chris Sparadeo    
C_802-369-4458 H_802-728-3059          -- 

 

Links:
------
[1]
http://members.sti.net/offgridsolar/
[2] mailto:[email protected]
[3]
mailto:[email protected]
[4] mailto:[email protected]
[5]
mailto:[email protected]
[6] mailto:[email protected]
[7]
http://californiasolarco.com
[8]
https://californiasolarco.com/referral_form/
[9]
mailto:[email protected]
[10]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[11]
http://www.mail-archive.com/[email protected]/maillist.html
[12]
http://www.re-wrenches.org/etiquette.htm
[13]
http://www.members.re-wrenches.org
[14]
mailto:[email protected]
[15]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[16]
http://www.mail-archive.com/[email protected]/maillist.html
[17]
http://www.re-wrenches.org/etiquette.htm
[18]
http://www.members.re-wrenches.org
[19] http://www.catamountsolar.com/
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to