Hi Jay,

Ray makes the right distinction between the PV system and other systems that I 
think applies to your example. This was the big change in 2017 as we pulled all 
the non-PV stuff out of 690 and created 706, 710, etc. The PV system disconnect 
is what you identify it to be though. Article 690 doesn’t tell you what 
disconnect is the PV system disconnect, just that one must be identified per 
system. Also there is no limit on the number of disconnects in a PV system, so 
you could have one local disconnect located at an array for servicing etc but 
then add another one someplace else and identify that one as the PV system 
disconnect if you wanted. The system disconnect is the final one that separates 
the PV system from other system conductors. Other disconnects found in a system 
are typically equipment disconnects for servicing etc.

690.12 Rapid Shutdown only applies to circuits energized by PV sources, not 
circuits energized by other sources such as a utility, a battery, or a 
generator. The justification for RS was to protect firefighters working in or 
on buildings performing emergency operations. So if a PV array is attached to 
the building (not just on a roof, but for example an awning) then 690.12 
certainly applies. For a ground mounted system the answer is “it depends”. If 
the circuits energized by the PV array do not enter the building (i.e. a PV 
system ending at an outdoor battery shed) then it doesn’t. If a dc circuit 
comes from the PV array and enters a home then you need a means to bring that 
circuit below 30V before attaching to, or entering, the home. That might be a 
readily accessible disconnect (marked as an RS initiation device) not mounted 
on the home or some type of remote relay (listed to 1741 RS) operated by an RS 
initiation switch on the home.

The NEC 2020 language regarding 690.12 hasn’t changed that much. The most 
significant change is to further clarify what conductors must be controlled in 
690.12(A). That new language and informational note may help some struggling 
with this issue though. The other changes mainly improve the application of the 
new draft UL3741 standard to the inside array requirements.

Note that in both 2017 and 2020 there should be no inside the array 
(690.12(B)(2)) requirements for any ground mounted system not attached to a 
building. I hope no other people out there are suggesting there are. That was 
never identified as a requirement for 690.12. If an inspector in your area 
wants that I would personally have a prolonged discussion about that. I don’t 
think that position is supported by the Code language, or public record on the 
debates around this issue. It’s not a who’s “right” or “wrong” debate. It is 
simply how to apply the Code to the installation.

Also a heads up to look at new 2020 language in 480, 706, 692, 694, and even 
445, requiring the disconnection of all onsite sources from buildings. For 1&2 
family dwelling these disconnects must be outside. This parallels the new 
requirement for outdoor disconnects for utility services outside of these 
buildings. These new requirements close the loops that can concern in others 
about what happens to other circuits when I initiate RS for a PV array. None of 
these requirements are rapid shutdown though. It is all about de-energizing 
feeders and branch circuits in buildings. I think these requirements will often 
apply to off-grid systems. They are pretty straightforward though since the 
requirements are much higher level and not as prescriptive as 690.12.

I realize the 2017 (or probably 2020) language isn’t 100% clear. It never seems 
to be unfortunately. While I won’t say the language is “correct”, the way I 
describe these issues above is in line with the public inputs/comments/debates 
during the Code panel’s (CMP-4) development process, starting in 2014 and 
continuing to 2020. If anyone has specific ideas for 2023 improvements please 
let me know.

Hope some of that helps you all.

Jason Fisher
[email protected]


________________________________
From: RE-wrenches <[email protected]> on behalf of Ray 
<[email protected]>
Sent: Monday, September 30, 2019 1:40 PM
To: [email protected]
Subject: Re: [RE-wrenches] Module-Level Shutdown for off grid systems


The PV system (and 690.12) stop at the PV Disconnect. (see figure 690.1(b), 
Note (2)).  Charge Controllers are part of the Energy Storage system (706) now. 
 We presented this in our plan sets, and we drew clear lines on the wiring 
diagram showing which articles applied to which parts of the system.  The AHJs 
have not challenged us on this. However, they pulled a bunch of other stuff 
out, for instance that 705 still applies to off grid....

I still have not seen a good presentation anywhere on applying NEC 2017 to off 
grid, outside of the RE Wrenches list.  Everyone is still figuring this all out 
for off grid after all the changes in 2017.  Can't wait to see what 2020 looks 
like....

Ray WaltersRemote Solar303 505-8760

On 9/28/19 11:33 AM, jay wrote:
HI Jason

Does that mean that 690.12 B 1 would apply with the following.

A ground mounted or external array to a living structure
and
if the CC was less than 1 meter from entry into the building

You wouldn’t need rapid shut down?

jay
peltz power


On Sep 27, 2019, at 6:56 PM, Jason Fisher (STC) 
<[email protected]<mailto:[email protected]>> wrote:

Just a reminder to everyone struggling with this issue that only 
building-attached circuits energized by PV sources require RSD. So ground 
mounts generally don’t, or at least would only require a disconnect at the 
building if sending dc circuits into buildings.

Energy Storage is covered under article 706 in 2017 and does not require any 
shutdown, just sensible disconnection requirements.

Jason Fisher

________________________________




_______________________________________________List sponsored by Redwood 
AllianceList Address: 
[email protected]<mailto:[email protected]>Change
 listserver email address & 
settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive:
 
http://www.mail-archive.com/[email protected]/maillist.htmlList 
rules & 
etiquette:www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>Check
 out or update participant 
bios:www.members.re-wrenches.org<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios: