Hi Jeff,
Seems to me if allowed in your jurisdiction, you might be best served by installing a new 200A fused service disconnect ahead of the existing main service panel. Or even a 400A one to allow for additional work inside (CT’s), then perform a supply side connection in it. Some manufacturers of switchgear have an option for lugs that accept multiple conductors, so no piercing of conductors needs to happen. Good luck, Glenn From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of Jeff Clearwater Sent: Thursday, October 17, 2019 3:20 PM To: RE-wrenches <re-wrenches@lists.re-wrenches.org> Subject: [RE-wrenches] SolarReady Service Panel vs adding Supply Side connection? Esteemed Wrenches, I am in need of changing out an existing 200 Amp service entrance in order to accommodate a bus capable of handling a a 200 Amp Solar backfeed (41 KW system) . PG&E is upgrading the transformer to handle the backfeed but when I proposed a Siemens SolarReady 400 Amp service entrance they couldn't approve it cause since the building is a shop - they classify it as commercial and require a panel that can handle CTs when there is a 400 Amp service involved. Anyone else faced with this have solutions? What is the cheapest equipment I can provide to satisfy all requirements? We don't need to upgrade the existing 200 amp service entrance equipment for load purposes - only to meet the bus requirements of backfeed. Would it be cheaper and easier to use the existing (or new) 200 Amp residential panel - not call it a 400 Amp upgrade but simply add a 200 Amp Supply Side Connection? Suggested equipment to do that in the most economical manner? Any help well appreciated! Jeff -- ~~~~~~~~~~~ Jeff Clearwater Village Power Design linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/> www.villagepowerdesign.com <http://www.villagepowerdesign.com> cell - 413-559-9763 ~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org