They are not asking for 400 Amps - I suggested it as that was the rating of the solar ready panel I specified.

They are just saying IF it's 400 Amps then they need room for CTs cause it's a shop and hence residential equipment is not approved.

So as August and Glenn indicate below - perhaps the easiest is a 200 AMP meter can with a Supply side line.  That does throw it back to my AJH to approve but that is pretty standardI would hope.  It also requires the variance letter from PG&E.

I'm running 5 SB7.7s at 32 Amps each - so 160 AMPS of solar input.

So If I supply a 200 A meter can with supply side lugs that I can feed into a 200 A fused disconnect and solar distribution panel and keep the existing 200 Amp panel box fed by the 200 Amp main breaker - any reason that won't work?

OR does anyone know of a commercial 400 AMP solar ready meter base with 2 200 Amp feeds - one for solar and one for loads that does allow room for CTs?

Thanks,

Jeff

August Goers wrote on 10/17/19 4:35 PM:

Hi Jeff -

PG&E defines the service rating amperage based on the enclosure rating of the first piece of equipment the service hits. See section 1.14 in the Greenbook:

https://www.pge.com/includes/docs/pdfs/mybusiness/customerservice/startstop/newconstruction/greenbook/servicerequirements/greenbook_manual_full.pdf

This might be why they insist that you need a 400 A service just because you want a 400 A rated bus. The easy way around it is to supply a 200 A rated meter socket and main disconnect, then feed a 400 A sub panel.

A meter/main like the Eaton MBEB200BTS might also work for you: https://www.homedepot.com/p/Eaton-200-Amp-BR-Type-Main-Breaker-Meter-Breaker-without-Distribution-EUSERC-MBEB200BTS/100555147

August
Luminalt


Hi Jeff,

Seems to me if allowed in your jurisdiction, you might be best served by installing a new 200A fused service disconnect ahead of the existing main service panel. Or even a 400A one to allow for additional work inside (CT’s), then perform a supply side connection in it. Some manufacturers of switchgear have an option for lugs that accept multiple conductors, so no piercing of conductors needs to happen.

Good luck,

Glenn
On Thu, Oct 17, 2019 at 12:19 PM Jeff Clearwater <je...@villagepowerdesign.com <mailto:je...@villagepowerdesign.com>> wrote:

    Esteemed Wrenches,

    I am in need of changing out an existing 200 Amp service entrance
    in order to accommodate a bus capable of handling a a 200 Amp
    Solar backfeed (41 KW system) .

    PG&E is upgrading the transformer to handle the backfeed but when
    I proposed a Siemens SolarReady 400 Amp service entrance they
    couldn't approve it cause since the building is a shop - they
    classify it as commercial and require a panel that can handle CTs
    when there is a 400 Amp service involved.

    Anyone else faced with this have solutions?  What is the cheapest
    equipment I can provide to satisfy all requirements?

    We don't need to upgrade the existing 200 amp service entrance
    equipment for load purposes - only to meet the bus requirements of
    backfeed.

    Would it be cheaper and easier to use the existing (or new) 200
    Amp residential panel - not call it a 400 Amp upgrade but simply
    add a 200 Amp Supply Side Connection?  Suggested equipment to do
    that in the most economical manner?

    Any help well appreciated!

    Jeff








-- ~~~~~~~~~~~
    Jeff Clearwater
    Village Power Design
    linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
    www.villagepowerdesign.com <http://www.villagepowerdesign.com>
    cell - 413-559-9763
    ~~~~~~~~~~~~~~~~~~~~~~~
    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to