Hey Jay,

Yes so you were on to it - but with the addition of having that downstream of a separate 200 AMP meter box and 200 A Main that works :) Otherwise PG&E would call it a 400 Amp service which for commercial accounts means having to have CTs for the metering.

Thanks!,

Jeff

Jay wrote on 10/17/19 3:38 PM:

What about installing a 200 amp breaker in the 400 amp buss box?

We talk a lot about doing it for smaller boxes, is there a reason it won’t work here?

Jay
Peltz power

On Oct 17, 2019, at 1:30 PM, Glenn Burt <[email protected]> wrote:



Hi Jeff,

Seems to me if allowed in your jurisdiction, you might be best served by installing a new 200A fused service disconnect ahead of the existing main service panel. Or even a 400A one to allow for additional work inside (CT’s), then perform a supply side connection in it. Some manufacturers of switchgear have an option for lugs that accept multiple conductors, so no piercing of conductors needs to happen.

Good luck,

Glenn

*From:*RE-wrenches <[email protected]> *On Behalf Of *Jeff Clearwater
*Sent:* Thursday, October 17, 2019 3:20 PM
*To:* RE-wrenches <[email protected]>
*Subject:* [RE-wrenches] SolarReady Service Panel vs adding Supply Side connection?

Esteemed Wrenches,

I am in need of changing out an existing 200 Amp service entrance in order to accommodate a bus capable of handling a a 200 Amp Solar backfeed (41 KW system) .

PG&E is upgrading the transformer to handle the backfeed but when I proposed a Siemens SolarReady 400 Amp service entrance they couldn't approve it cause since the building is a shop - they classify it as commercial and require a panel that can handle CTs when there is a 400 Amp service involved.

Anyone else faced with this have solutions?  What is the cheapest equipment I can provide to satisfy all requirements?

We don't need to upgrade the existing 200 amp service entrance equipment for load purposes - only to meet the bus requirements of backfeed.

Would it be cheaper and easier to use the existing (or new) 200 Amp residential panel - not call it a 400 Amp upgrade but simply add a 200 Amp Supply Side Connection? Suggested equipment to do that in the most economical manner?

Any help well appreciated!

Jeff







--
~~~~~~~~~~~

Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to