Of course then there is the "bottom line", final say approval determined
by the AHJ which might be hard for this inspector to refuse your
clearances when he/she is asked to operate that switch and see that
there is zero issue with its safe and easy operation. AHJ's are allowed
to use common sense.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net
On 3/11/2020 3:03 PM, Jason Szumlanski wrote:
I'm meeting him tomorrow. He tells me it's too close but I can't get
him to tell me what an acceptable distance would be. It's totally
insane. I was pretty sure there was nothing in the NEC about this
specifically, but I wanted to make sure before I asked him to cite a
code reference in his rejection letter so I could appeal it to the chief.
*
*
On Wed, Mar 11, 2020 at 5:52 PM Chris Sparadeo
<[email protected] <mailto:[email protected]>> wrote:
I've looked through Article 110 and even UL listings for GE
disconnects and there is no specific code of reference to minimum
space about the component (other than typical working space
requirements). Ask your AHJ to point to a code reference...
On Wed, Mar 11, 2020 at 4:42 PM Jeff Clearwater
<[email protected]
<mailto:[email protected]>> wrote:
Yes, what others said - my understanding is that as long as
the door can open 90º then it's considered not in the way of
working space.
Jeff Clearwater
--
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org