Christopher;


Just spit-balling here:  is the secondary inverter asleep (hate the
master/slave terminology…)?  Try changing power save settings to make sure
the secondary is awake and see if that changes the situation.  Seems
unlikely this will solve the problem, but it may provide some kind of clue.



Also, did you try swapping primary and secondary?  Run with secondary alone
as primary?



William Miller



*From:* RE-wrenches [mailto:[email protected]] *On
Behalf Of *Chris Schaefer
*Sent:* Thursday, June 25, 2020 10:35 AM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s



G'Day All,



So I started up a system recently with two Radian 8048A's. The master is
connected to port 1 and the slave connected to port 2 with the FlexNet at
port 3. There are no OB charge controllers in the system. When the hub is
polling (led's scrolling) nothing shows up for the slave at port 2. It's
like the slave inverter doesn't exist. So I moved the slave and flexnet
down to port 3 and 4. No change in the polling. I swapped out comm (factory
green) cables. Again no change. Looking at the control board of the slave
there is only one green led on which is located at the upper right-hand
side. Otherwise no led's are on. I have 57v at the buss bar terminals of
the inverter. Of course since there is no polling at the hub there is no
way to view port 2 to view the slave at the Mate.



Now the only thing that I didn't do was to try and use the manual on/off
switch-jumper to start the slave. But in the past regardless of the
inverter being on or off it would still show up on the hub. This is  a new
one and I'm looking for some direction here.



Thanks,

Christopher-

Chris Schaefer’s
<http://www.solarandwindfx.com>

*Tel/Fax 585-229-2083 or Cell 585-748-1870 *
*5115 South Hill Road ~ Canandaigua New York 14424www.solarandwindfx.com
<http://www.solarandwindfx.com> ~ E-mail: **[email protected]
<[email protected]>*

Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to